Results 1 to 8 of 8
    I ordered a 3.5-5 ton Goodman TXV
    I have the same senario with the exact same P/N condenser and a Goodman 3.5 ton ARUF air handler. The system is cooling, pressures look good, but cannot satisfy below 79 degrees in the heat of the day (central Florida, summer). I just ordered a Goodman 3-5 ton TXV kit. Did the TXV resolve your issue?
    Mar 2012
    West Chester, PA
    you should have a txv to match the outdoor unit (capacity and refrigerant type)
    Quote Originally Posted by ADillon View Post
    Great, I ordered a 3.5-5 ton Goodman TXV for R-22 based on advise from another more experienced tech. The outdoor unit is a 3 ton R-22 unit. What will be the outcome of using this 3.5-5 ton TXV?
    Fort Worth, TX
    Quote Originally Posted by jroper630 View Post
    It might overfeed the evaporator. It might not. If you install it and don't check superheat or subcooling, you'll never know if it is or not.
    Building Physics Rule #2:
    Building Physics Rule #3:
    Mar 2012
    West Chester, PA
    I don't know goodman usually there is a txv that does a variety of sizes like 1.5-3 ton then it steps up to another txv that does 3.5-4 and then another that does 5. just as an example. So if you are using the next size up from what you need, it might overfeed. It is hard to tell what the outcome will be with mix matched units
    Made this its own thread. You are not allowed to post in other peoples threads, in the AOP forums. please read our site rules, thank you.
    On the Goodmana's some of the txv's need to be adjusted . It does take some time and effort
    Cincinnati, Oh
    the outcome is not good.
    "Just get it done son."
    Dad adjusted
