I ordered a 3.5-5 ton Goodman TXV
I have the same senario with the exact same P/N condenser and a Goodman 3.5 ton ARUF air handler. The system is cooling, pressures look good, but cannot satisfy below 79 degrees in the heat of the day (central Florida, summer). I just ordered a Goodman 3-5 ton TXV kit. Did the TXV resolve your issue?
-
08-09-2012, 10:15 AM #2
you should have a txv to match the outdoor unit (capacity and refrigerant type)
-
08-09-2012, 11:31 AM #3
New Guest
- Join Date
- Aug 2012
- Posts
- 2
-
08-09-2012, 11:58 AM #4
-
08-09-2012, 03:19 PM #5
I don't know goodman usually there is a txv that does a variety of sizes like 1.5-3 ton then it steps up to another txv that does 3.5-4 and then another that does 5. just as an example. So if you are using the next size up from what you need, it might overfeed. It is hard to tell what the outcome will be with mix matched units
-
08-09-2012, 05:12 PM #6
Made this its own thread. You are not allowed to post in other peoples threads, in the AOP forums. please read our site rules, thank you.
-
08-09-2012, 08:29 PM #7
Professional Member*
- Join Date
- Jul 2006
- Location
- Virginia
- Posts
- 3,705
On the Goodmana's some of the txv's need to be adjusted . It does take some time and effort
-
08-09-2012, 08:57 PM #8
the outcome is not good.
"Better tell the sandman to stay away, because we're gonna be workin on this one all night."
"Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."
"Just get it done son."
Dad adjusted