    Goodman compressor failure?

    I’ve got a problem with a new Goodman AC. The system works great for 30 minutes but then the compressor stops running but the condenser fan is still running. When I turn the system of and on again the condenser fan starts but the compressor makes a humm sound and then a second or so later stops. It is as if the compressor is stuck. The next day it will do the same thing all over again. Run good for 30 minutes and then stop. Does anyone have any idea what problem is?

    Details:
    New 3Ton R22 split system
    Goodman compressor w/ hard start kit and coil with TXV.

    77/190 PSI
    superheat = 7 F
    supercool = 9 F

    When running: 1419 cfs, 95 F outside, 86 F inside, 61 F from vents --> 25 F cooling

  2. #2
    Join Date
    Dec 2008
    Location
    Ontario Canada
    Posts
    363
    What are your pressures when it tries to start again?

    Compressor a scroll or recip?

  3. #3
    Join Date
    Aug 2012
    Posts
    9
    pressure when compressor is not running: about 130 PSI on both high and low side
    pressure when compressor is running: 77 PSI low side and 190 PSI on the high
    It's a recip compressor.


    Quote Originally Posted by LKJoel View Post
    What are your pressures when it tries to start again?

    Compressor a scroll or recip?

  4. #4
    Join Date
    Jul 2006
    Location
    Brooklyn , NY
    Posts
    24
    Can you check pressure and amps on compressor in moment when compressor stop running.

  5. #5
    Join Date
    Aug 2012
    Posts
    9
    Quote Originally Posted by valentyn View Post
    Can you check pressure and amps on compressor in moment when compressor stop running.
    That would be an interesting test. I’d have to get a new multimeter that does measures current and I’d have to watch the system for 30 minutes and wait for the precise moment it stops. What would be the sign of a bad compressor? Thanks

  6. #6
    Join Date
    Jul 2006
    Location
    Brooklyn , NY
    Posts
    24
    Quote Originally Posted by RJ777 View Post
    That would be an interesting test. I’d have to get a new multimeter that does measures current and I’d have to watch the system for 30 minutes and wait for the precise moment it stops. What would be the sign of a bad compressor? Thanks
    It`s depend what you reading.

  7. #7
    Join Date
    Jul 2007
    Location
    Delaware
    Posts
    3,452
    77/190?
    Always here

  8. #8
    Join Date
    Jan 2012
    Location
    indy
    Posts
    460
    Quote Originally Posted by RJ777 View Post
    I’ve got a problem with a new Goodman AC. The system works great for 30 minutes but then the compressor stops running but the condenser fan is still running. When I turn the system of and on again the condenser fan starts but the compressor makes a humm sound and then a second or so later stops. It is as if the compressor is stuck. The next day it will do the same thing all over again. Run good for 30 minutes and then stop. Does anyone have any idea what problem is?

    Details:
    New 3Ton R22 split system
    Goodman compressor w/ hard start kit and coil with TXV.

    77/190 PSI
    superheat = 7 F
    supercool = 9 F

    When running: 1419 cfs, 95 F outside, 86 F inside, 61 F from vents --> 25 F cooling
    better check that pot relay on that start kit, if it;s stuck closed that start winding is overheating, nott likely it would run a half hour but it could I guess, if your not sure take it off and see that way, prob doesnt (have to have it) but never hurts, exp if your press equalizes during off cycle. Also check amp vs.fla on chart, is it getting hot by the touch, need more info. Check cap and fan proformance, anything can be wrong on a new unit just like an old one, I have alot of new crap bad these days.

  9. #9
    Join Date
    Nov 2011
    Location
    Michigan
    Posts
    50
    If your sitting at 190 psi and it's 95 deg. out your not pulling any air through the condenser. Can you feel air coming out of the top?

  10. #10
    Join Date
    Aug 2001
    Location
    Pavilion, NY
    Posts
    1,652
    My money is on the cap.
    ...

  11. #11
    Join Date
    Jun 2006
    Location
    SW MO.
    Posts
    4,454
    Quote Originally Posted by upant View Post
    If your sitting at 190 psi and it's 95 deg. out your not pulling any air through the condenser. Can you feel air coming out of the top?
    If he wasn't pulling any air thru the condenser coil his head would be high. Very high.

    Besides new unit. Why wouldn't it be moving air?

    Recip on new unit?

    Did you release the nitrogen charge before vacuuming?

  12. #12
    Join Date
    Aug 2012
    Posts
    9
    You are right chaard. There is hot air coming out of the top. Kida has to since it’s blowing 25 F cooled air in the house. And yes it is a recip. The smaller Goodman models are still recip. Yes I did release the nitrogen before vacuuming.

  13. #13
    Join Date
    Nov 2011
    Location
    Michigan
    Posts
    50
    Quote Originally Posted by chaard View Post
    If he wasn't pulling any air thru the condenser coil his head would be high. Very high.

    Besides new unit. Why wouldn't it be moving air?

    Recip on new unit?

    Did you release the nitrogen charge before vacuuming?
    Ya, I could have thought that through but my point was. Why is there only a 3-5 degree condenser TD. Should be 15 to 20 degrees. So weak compressor or start cap.