    ...OK, so on the Goodman unit in the attic the Furnace control board was replaced, replaced blower run cap and installed condensate safety switch, test ran system, Freon levels were proper after 20 minutes or more of running and air coming out of vents was 20-F cooler than intake air.
    The indoor temp-split at first look, apparently, appears to be on target...it is always a good idea to also check the outdoor condenser temp-split, as it can verify the indoor split or reveal other problems.

    Also, what was the indoor airflow CFM & Return Air humidity level, & the superheat & subcooling; because if the humidity was much lower or higher than 50% RH, & other factors are off target then, the indoor split may not actually be on target.

    The only way U will know is if the system is checked much further than one factor...
    Last edited by udarrell; 08-09-2012 at 09:48 PM. Reason: Words missing...

  3. #29
    Join Date
    Apr 2003
    Location
    phoenix, AZ single family one story residence
    Posts
    17
    the a/c circuit board seems to have been the correct fix.
    COLD air now that works .
    YES, Thank you for everyone's thoughts.

Page 3 of 3 FirstFirst 123

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event