Hey Darrel and HVAC community...
I just wanted to give you all an update...I had a good company come out and increase the size of two of the return runs and the riser (now rectangular ductboard), and replaced the mixing box...they also needed to add 4.5 LBs of freon (which surprised me) and re-adjusted the blower profile to 20° F split across the coil...wow...what a difference! The house is now cooling at whatever temp I set it to (75° F) and is operating at normal pressures etc.
Thanks again to everyone for your advice and suggestions.