    Hi…my name is Mike and we live in a single-level/5 Bedroom/3 Bath - 2758 SQFT “Nohl Crest” Carrington floor model home located in Tampa Bay, FL – contrary to popular belief, the temperature & humidity here are not as bad as other parts of the country…with that said – the weather has been averaging around 91° F with about 65-75% humidity so far this year. I am the owner of a newer “Amana” heat pump system (2.5 Years – 3rd season) installed February of 2010:
    Note*
    • Refrigerant lines were not replaced from the coil to compressor
    • Flex-duct – they replaced one 25’ supply run in attic and approx. 10’ of 18” return flex next to blower
    • After the unit was first installed…this AC company had to make three return trips within the first few months:
    1. The first trip was the very next day as they installed the blower crooked and it looked like the Leaning Tower of Pisa sitting on the plenum
    2. The second trip was during the first summer season in August of 2010 – the circuit board in the air handler & heat pump, contactor, transformer, RV coil & thermostat were all (unexplainably by technician) to have gone bad and were all replaced.
    3. Four more months later…a third return trip was necessary as the “Defrost Board” was not energizing on the terminal and was replaced as bad
    Issue:
    The indoor temperature will not cool below 79° F…intermittently; it doesn’t matter if its overcast outside either…it’s just intermittent regardless of the sun exposure/temperature outside. So I contacted the AC company who installed the system to take a look…the HVAC technician tested the compressor discharge & liquid line temps and told me that everything was fine and that the temp diff was normal for this time of year due to the heat index . I told him that my home was adequately insulated with a new roof and has always cooled to whatever the thermostat was set to…and even in the hottest months! I also told the HVAC technician that the condensate drain was backed up a bit with algae…so I went ahead and completely flushed the line just before he got there…but then he said that we should just wait it out, since the drain may have caused the issue; although, it took 4-5 hours (and nightfall) – the indoor temp eventually dropped to a comfortable 74° F. - that was last week…over the last few days…again the cooling has been intermittently going from 74° F (my setting) on some days and 79° F on others. This is only a 12° drop from outside temps…
    My Questions to this Forum:
    The unit/labor is warranted for 10 years so I don’t foresee an issue, but what do I tell this company? What do I ask them for as far as service expectations? What type of testing and service should I expect? I would like to sound somewhat educated on the subject in the event that the same technician comes out and tries to snow me or talk me out of something that is not covered under warranty.
    Also…can anyone tell me whether or not the system I purchased is adequate for my home and whether Amana is even a reputable/quality product? (I get conflicting opinions on this)
    I am just looking for some advice…any and all input is welcome.
    Thank you for your time,
    BDC
    Jan 2012
    WEST COLUMBIA S.C.
    2750square feet and 2.5 tons.That is a question by it self. I don't care if the house is covered with bushes
    The Amana brand is not your problem.
    Looks like the installer is the problem.
    Replaced board, blower, contactor, transformer, coil, and wire?
    WOW.
    See if you can find a different Amana dealer that can actually find the problem and fix it.
    Quote Originally Posted by hewitt View Post
    He posted the model number of a 5 ton unit. Its been in for 2.5 years, its on its third season.
    Jan 2012
    WEST COLUMBIA S.C.
    X2.u have a parts changer
    Tampa Bay
    I was hoping more members would have responded to this post by now as the house was really warm this last week (we have computer equipment throughout the place to do our jobs) I was as thorough with my explanation as possible and would have provided more if needed; again...I was just looking for some answers and some advice.
    So I just took your advice "2Old2Rock" and hired a NATE certified company to do a diagnostic today.
    Jun 2005
    SW Wisconsin
    Quote Originally Posted by THE_BDC View Post
    In addition to the other checks the Tech takes, - make sure he checks the compressor discharge line temp.
    The compressor's discharge temperature should be measured about 1 to 2 inches away from the compressor on the discharge line. This discharge temperature should never exceed 225°F. Carbonization and oil breakdown can occur if compressor discharge temperatures exceed 225°. There is also a temp it should not go below.
    The three causes for high discharge temperatures are:
    High condensing temperature.
    Low evaporator pressures and temperatures.
    High compression ratios.
    There is a long list of causes & effects within those above categories...
    Tell the Tech you want a documented list of the test data he/she collects!
    Last edited by udarrell; 08-13-2012 at 01:06 PM. Reason: a documented list of the test data Tech collects
    AOP Forum Rules:
    Rules for Posting
    Rules For Equipment Owners
    Equipment Owners Find a Contractor HERE!
    Free online whole house load calculator & Sizing: http://www.loadcalc.net/ Anyone can use it...!
    udarrell
    Tampa Bay
    Hi Darrel,
    Thanks for responding (and the other techs above too)...I had another company come out and they dont think (at least not yet) that its a refrigerant issue as the circuit is good, valve is opening and appears to be condensing good - no high discharge temperatures etc.
    They feel that it is Air-Flow related as he found an issue with the air-flow in my return ducting being low on the suction side and was .9 negative pressure on the return by itself....he said the total external should be around .6! So...they want to come back out and change out the return riser etc. The 5 ton I have now was an upgrade from a 4 or 41/2 ton...so the previous company didn't change out any of the return duct and they didnt use the right size on the riser which ties into a mixing box in the attic.
    Since this is load-based and not getting the right air flow....they said that they really cant get an accurate reading but are suggesting I take these first steps. Do you or anyone have anymore feedback on this before I make a decision?
    Again...thanks to all that replied.
    Quote Originally Posted by udarrell View Post
    Jun 2005
    SW Wisconsin
    Hi Darrel,
    Wow, .9" of an inch on the Return Side alone is terrible; the negative Return side is added to the Supply Side for the total static which should be .5" or as he said .6" tops.
    The 2.5%m summer design in Tampa FL is 91-F dry bulb; 77-F wet bulb for a high 54% RH; at that 91-F which means a loot of grains of moisture per lb of air to be removed by the A/C. That is a reason not to oversize the system.
    Yes, that Return Air problem has to be properly resolved for the system to begin to cool properly. Get it done right & then check & balance the charge to the new higher heatload on the indoor coil.
    AOP Forum Rules:
    Rules for Posting
    udarrell
    Tampa Bay
    I heard that before...and was a little concerned about the 5 ton replacing the old 4.5 ton in my 2758 SQFT home...as the rule of thumb dictates - 600 p/ton? or was it 500 SQFT?
    One point still eludes me...why didn't I have any issues the first two seasons?
    Anyhow...thanks for the advice and after the repairs are made to the return...I will drop by to post the results.
    Tampa Bay
    Hey Darrel and HVAC community...
    I just wanted to give you all an update...I had a good company come out and increase the size of two of the return runs and the riser (now rectangular ductboard), and replaced the mixing box...they also needed to add 4.5 LBs of freon (which surprised me) and re-adjusted the blower profile to 20° F split across the coil...wow...what a difference! The house is now cooling at whatever temp I set it to (75° F) and is operating at normal pressures etc.
    Thanks again to everyone for your advice and suggestions.
    BDC
    Jul 2009
    South Carolina
    Fool me once, shame on you. Fool me twice shame one me.
    Gary
    http://www.oceanhvac.com
    The best things in life are free but not everyone is willing to pay the price.
    Tampa Bay
    Quote Originally Posted by garyed View Post
    That's very clever...but not very helpful, what else ya got? - thanks.