08-07-2012, 03:48 PM #14
You might try and collect the condensate comming from the unit in question to determine whether the unit is removing the proper amount of moisture from the air. If it is, then you would obviously need to look into where the excessive amount of moisture is comming from-internally, externally or both. A pro here called Teddybear has a formula you can use that would be helpful.
An answer without a question is meaningless.
Information without understanding is useless.
You can lead a horse to water............
http://www.mohomeenergyaudits.com
-
08-07-2012, 04:34 PM #15
temp deltas should be taken at the air handler.
Your duct work has some leakage, no such thing as zero leakage.
-
08-07-2012, 07:28 PM #16
Professional Member*
- Join Date
- Dec 2005
- Posts
- 1,655
The humidity level is at the the grill where the air the blowing out ??????
If it is from the supplying grills then, the humidity readings for the 2 good units are very strange.
If not (which mean the air in the room/area), then the data for the large unit is very strange too.
Please clarify the data one more time.