Thread: Humidity issue

  1. #14
    Join Date
    Sep 2009
    Location
    Arnold mo
    Posts
    3,788
    You might try and collect the condensate comming from the unit in question to determine whether the unit is removing the proper amount of moisture from the air. If it is, then you would obviously need to look into where the excessive amount of moisture is comming from-internally, externally or both. A pro here called Teddybear has a formula you can use that would be helpful.
    An answer without a question is meaningless.
    Information without understanding is useless.
    You can lead a horse to water............
    http://www.mohomeenergyaudits.com

  2. #15
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    66,769
    temp deltas should be taken at the air handler.

    Your duct work has some leakage, no such thing as zero leakage.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #16
    Join Date
    Dec 2005
    Posts
    1,823
    Quote Originally Posted by falkirk18 View Post
    ...

    So, Since I've had the a/c company out twice, and they told me nothing was wrong, I bought a humidity gauge and started some testing of my own. On the two units that seem to be able to maintain a comfortable level of humidity, these are readings: supply temp of 10-16 degrees below return air temp and humidity level at supply of 30-40%. On the unit I feel is malfunctioning, I am getting a supply temp of 10-16 degrees below return air temp, but the humidity levels are 75-90%.
    ...

    Thanks in advance for your help!
    The humidity level is at the the grill where the air the blowing out ??????

    If it is from the supplying grills then, the humidity readings for the 2 good units are very strange.
    If not (which mean the air in the room/area), then the data for the large unit is very strange too.

    Please clarify the data one more time.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event