Results 1 to 9 of 9

Thread: Alerton to AX

  1. #1
    Join Date
    Oct 2009
    Posts
    856
    Post Likes

    Alerton to AX

    I was able to find some old submitals of a clients building. It looks like there is an alerton IBEX system in the building. I have never worked on these controls and the original contractor is out of the picture. I'd like to propose an integration option into AX. Is there anyway to bring this into an FX60? If so, has anyone accomplished this? From what I'm reading it doesn't seem to be the easiest thing. I'm also open to any other options/suggestions. Thanks in advance.

  2. #2
    Join Date
    Mar 2007
    Posts
    501
    Post Likes
    If you can get your hands on a BCM-TUX and the alerton software, it can be done. It is extremely time consuming though. Other than that, I don't believe there is any other option.

  3. #3
    Join Date
    Dec 2006
    Location
    What? Who? Where?
    Posts
    2,101
    Post Likes
    You would think that seeing Honeywell owns Alerton and Tridium they would develop a driver for the TUX protocol.

    kontrol out
    "Good" - Jocko
    "Open is as open does." - Forrest Gump
    "Can't we all just get a Lon?" - Garry Jack
    "BACnet: integration or interrogation?" - The Janitor
    "Open protocols? You can't handle open protocols!" - Nathan R. Jessup
    “What’s that? Aaa… open protocols? Don’t talk about…. open protocols? Are you kidding me? Open protocols? I just hope we can hardwire an interface!” - Jim Mora Watch it here!

  4. #4
    Join Date
    Mar 2008
    Location
    Council Bluffs, Iowa
    Posts
    128
    Post Likes
    There was a little disscussion a while back about developing the driver for this. I dont think that it will happen because these controls are being phased out now. If you can get your hands on the BCM-Eth, BCM-Pwr, and BCM-Tux, it would be easy to accomplish this. The controllers would be routed to the Jace through either Bacnet/IP or Bacnet Ethernet, your choice, and then they will discover as individual controllers. If you are dealing with App specific controllers, I.E. Tx-Vav, Tx-SA, then the points list will be the same for all controllers.

    If they are programmable controllers, then you are going to need some help to reverse engineer the programming to develope the points list. Unless you are lucky to have some documentation that has this info.

  5. #5
    Join Date
    Apr 2012
    Posts
    116
    Post Likes
    I will need VisualLogic to program BCM. And probably IBEX TDS to read programs from existing controllers in case there are no point lists available.

  6. #6
    Join Date
    Mar 2007
    Posts
    501
    Post Likes
    Quote Originally Posted by CB_Matt View Post
    There was a little disscussion a while back about developing the driver for this. I dont think that it will happen because these controls are being phased out now. If you can get your hands on the BCM-Eth, BCM-Pwr, and BCM-Tux, it would be easy to accomplish this. The controllers would be routed to the Jace through either Bacnet/IP or Bacnet Ethernet, your choice, and then they will discover as individual controllers. If you are dealing with App specific controllers, I.E. Tx-Vav, Tx-SA, then the points list will be the same for all controllers.

    If they are programmable controllers, then you are going to need some help to reverse engineer the programming to develope the points list. Unless you are lucky to have some documentation that has this info.

    Easy if someone didn't write 5000 global ddc and ibex points in the apex.

  7. #7
    Join Date
    Mar 2008
    Location
    Council Bluffs, Iowa
    Posts
    128
    Post Likes
    Quote Originally Posted by noskilltech View Post
    Easy if someone didn't write 5000 global ddc and ibex points in the apex.
    This does not make it any tougher to do the swap. You will not need the Ibex points any longer, so they can go away. If they are application specific you will not need most of the global ddc, which was there mainly for display purposes.

  8. #8
    Join Date
    Oct 2009
    Posts
    856
    Post Likes
    Thread Starter
    Thanks for all the info. It looks like I'm going to propose a whole new control system.

  9. #9
    Join Date
    Mar 2008
    Location
    Council Bluffs, Iowa
    Posts
    128
    Post Likes
    Quote Originally Posted by Igotworms View Post
    Thanks for all the info. It looks like I'm going to propose a whole new control system.
    Good Choice.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.