Results 1 to 5 of 5
  1. #1

    Dynamic AirFlow Troubles! Plz help

    I am a Clean Room Specialists and am having some issues with a dynamic system which is being controlled by Price vav's at which are attempting to maintain a negative pressure and constant flow in a space. I have noticed at times that the DP varies although flows are being maintained and duct static pressures are maintained.

    The system varies from -.06(ideal) to -.09(life safety concern) however like I said the flow rates have negligible change no more than about 35cfm on a system that flowing 1200cfm. When the system pressure gets upwards of -.09 we have door closing issues. Any suggestions or information would be helpful.

    Thanks

    BB

  2. #2
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    62,194
    -.09(life safety concern)???

    There is more of pressure loss going from 0' elevation to 500' elevation.
    Contractor locator map

    How many times must one fix something before it is fixed?

  3. #3
    Its been determined that once the space starts to hit a -.1 it takes upwards of 60lbs of pull to open the door. In case of an emergency its a concern on whether a 4'10" 90lbs young lady can open the door or not.

  4. #4
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    62,194
    A 3'X7' door with a negative pressure of .1" holding it shut, would only have a total of 10.8 pounds of force against it.
    Contractor locator map

    How many times must one fix something before it is fixed?

  5. #5
    Join Date
    Aug 2012
    Location
    Gainesville, FL
    Posts
    227
    *
    Last edited by Pete838; 08-19-2012 at 12:10 PM.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •