Results 1 to 9 of 9

Thread: Silly question

  1. #1
    Join Date
    Dec 2001
    Location
    Phoenix, Az
    Posts
    1,250
    Post Likes

    Silly question

    If a sight glass is between the receiver and LL solenoid, shouldn't the sight glass be full when the solenoid closes? Why would it be empty?

  2. #2
    Join Date
    Jun 2010
    Location
    Miami
    Posts
    258
    Post Likes
    What makes you think it is empty?

  3. #3
    Join Date
    Dec 2001
    Location
    Phoenix, Az
    Posts
    1,250
    Post Likes
    You can watch it drain after the LLSV shuts

  4. #4
    Join Date
    Jun 2010
    Location
    Miami
    Posts
    258
    Post Likes
    That would be before...or after the compressor stops?

  5. #5
    Join Date
    May 2003
    Location
    Utah
    Posts
    746
    Post Likes
    Essentially you've got a finite volume (condenser, receiver and portion of liquid line) with some amount of refrigerant in it. For this to be 100% liquid, the refrigerant would need to be at a pressure that is equal to, or higher than the correspoding saturation temperature of the refrigerant.

    When the compressor stops the liquid pressure reduces. Likely you're seeing the pressure fall below the point where the refrigerant would remain as 100% liquid.

  6. #6
    Join Date
    Dec 2001
    Location
    Phoenix, Az
    Posts
    1,250
    Post Likes
    Quote Originally Posted by bunny View Post
    Essentially you've got a finite volume (condenser, receiver and portion of liquid line) with some amount of refrigerant in it. For this to be 100% liquid, the refrigerant would need to be at a pressure that is equal to, or higher than the correspoding saturation temperature of the refrigerant.

    When the compressor stops the liquid pressure reduces. Likely you're seeing the pressure fall below the point where the refrigerant would remain as 100% liquid.
    That makes sense. Thanks

  7. #7
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,159
    Post Likes
    Either that or the liquid is physically draining back into the receiver, seeking it's own level as any liquid will tend to do.

    This would depend on the piping orientation.

  8. #8
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,071
    Post Likes
    Have you ruled out magic yet?

    because I think it might be magic.

  9. #9
    Join Date
    Sep 2003
    Location
    North-Central Ohio
    Posts
    22
    Post Likes
    I think it's the magic effect. But seriously, I see this all the time and agree w/ bunny & jpsmith1cm.
    Worry about the site glass when box temp is close and the unit is running. Also pay close attention to SC and SH.