Results 1 to 13 of 17
Thread: Superheat
    Superheat
    Hi guys new here and need help
    I have been outside the hvac business for a while now but
    my brother asked me to install a new ductless unit (split) in his home
    well the indoor unit is the new piece i have installed
    the old one has a leak in the evaporator the outside unit is fine
    the unit needs to be charged with some f22
    so i am using the superheat meathod to charge it
    i just want to make sure if my calculations is right
    Outside temp: 113F
    Indoor temp: 80F
    required superheat: 33F
    _________________________________
    Low line Temp: 32
    Low line Pipe Temp: 19
    current superheat: 13
    should the superheat be 33F ???
    Apr 2012
    Paper Street Soap Company
    Ductless units only have one service port on the high side ( not a hp)
    How could you get ssh ?
    Low Line = Large Diameter pipe
    not the small one ( high side)
    suction pressure converted to temp: 32F
    suction line temp: 19F
    Fort Worth, TX
    Installation manual. Charging scale. Combine the two and see if your results improve. That's all we can really tell you here due to DIY restrictions of this section.
    Building Physics Rule #2:
    Building Physics Rule #3:
    I just want to know if 33 superheat is fine ?
    Mini-splits aren't charged by the superheat method.
    Read the manual.
    Oct 2002
    Plano, TX
    minisplits I work on have expansion device in the outside unit. Both pipes going to inside unit are suction. Service valve is suction. I'd feel fine with 10-20 SH.
    Quote Originally Posted by cuadro View Post
    So your suction line pressure is 58PSIG, and your suction line temp is 19F? Or is it 19C.
    Massachusetts
    Anytime a repair is done on a mini, you should recover the entire charge and weigh in a new charge after a thorough evacuation process. As stated by others, both lines in the lineset are normally insulated because the EEV is located inside the outdoor unit, thus the service tap is low side but before the evaporator and your gauge set is reading saturated pressure of evaporation, primarily at the indoor unit.
    Right
    We are Talking F
    We are Talking F
    Then I would think either your gauge or your temp probe is inaccurate. Since that would indicate that your suction line is losing heat.
    no my set is brand new and i have another one the same result is showing on both