Results 1 to 3 of 3
  1. #1

    Evaporator Replacement - looking for some professional advice

    Hi All:

    New guest and the first post. Got a 15 yrs old 5ton Carrier system (R22). Compressor was replaced 3yrs ago (under home owners warranty). Now the evaporator leaking so needs replacement. Before asking for quotes from my local HVAC professionals I would appreciate your thoughts on the followings:

    #1. Is there going to be any benefit to install a TXV when replacing the evap? Current evap has fixed orifice and 10+ SEER.


    #2. While reading online HVAC lits, I came across recommendations to add a P and inverted P trap on the suction line right at the outlet of the evap coil. My current system does not have the P traps on the suction line and worked fine so far. Should I ask the AC tech to add the P traps with the new evap? It's a single story house, the evap on the attic. The line is about 35 ft. 25 ft runs horizontal with about 2 ft drop and the rest 10 ft has about 8 ft vertical drop to the outside unit.

    Thanks in advance.

  2. #2
    Join Date
    Jun 2006
    Location
    Richmond, VA
    Posts
    2,872
    It's 15 years old, don't just replace the evap.

    Most new systems require a txv.

    Installer should follow piping instructions in installation manual and addendums.
    Give a man a fish, he will eat for a day. Teach a man to fish, he will eat for a lifetime.

    Give a man a capacitor, doesn't know what to do. Teach a man to install it, now he knows everything.

  3. #3
    Thanks beshvac

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event