    New LIEBERT discharge service valve hard to turn.

    I have a discharge service valve for a 06D semi comp to replace. The new one is very hard to turn with a service valve wrench. I want to be sure this is normal before installing it, in case the stem is bent. Anyone else find this the case?

  2. #2
    Join Date
    Oct 2001
    Posts
    6,636
    remove the packing nut and drip some refer oil into the cavity then reinstall packing.if not and in hand drip somr oil on the shaft and on the seat stem inside before install ...work it back and forth it is dry that's why
    "when in doubt...jump it out" http://www.youtube.com/watch?v=aMy-sAHwS4E

  3. #3
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    998
    Try backing the packing out a half turn, if you haven't already, open or close valve then tightened packing back to prevent leaking. If that don't help try the disassembly and oil. If both fail pitch it!! Good luck.