    Reversed coil???

    I had a brand new trane installed in april. I have been wondering why my humidity spikes everytime the unit turns on. Well I noticed a decent amount of water in the drain pan. I looked inside AH, and noticed insulation very wet, and looking inside i noticed the coil is reversed! The bottom of the "a" is facing the blower, return air is passing through the top of the"a". I see water dripping down...and I assume is blowing through the blower and into the ducts when its running, and i guess is why the pan is filled.. The coil sounds like its reversed...correct??? I will be calling installer tomorrow. Should i request a brand new AH since its been getting wet since april? Thoughts and suggestions please. Thanks.

  2. #2
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,630
    Post Likes
    Need pictures, but if the air handler is installed in the horizontal left position, the coil i supposed to be flipped with the apex of the coil facing into the return.

  3. #3
    Join Date
    Apr 2004
    Location
    long island
    Posts
    89
    Post Likes
    Thread Starter
    Quote Originally Posted by mark beiser View Post
    Need pictures, but if the air handler is installed in the horizontal left position, the coil i supposed to be flipped with the apex of the coil facing into the return.
    Supply----fan-coil>---------Return air
    Don't have pics at the moment, but my diagram shows my air handler. Return air comes from right, and coil "point" is as the diagram shows, then fan, then supply goes out left. Does this look correct? Or reversed?

  4. #4
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,630
    Post Likes

  5. #5
    Join Date
    Apr 2004
    Location
    long island
    Posts
    89
    Post Likes
    Thread Starter
    Quote Originally Posted by mark beiser View Post
    Yes.
    Thanks, any ideas why I have alot of moisture under the fan? The insulation is wet, and the emergency pan underneath has a decent amount of water.I will provide a link...on page 16....is a diagram. My unit has the coil reversed....WHY?
    http://crea.com.co/imagenes/PDF/Cat_...60_CATALOG.pdf

  6. #6
    Join Date
    Feb 2006
    Location
    Float'N Vally, MS
    Posts
    2,533
    Post Likes
    Quote Originally Posted by suzook View Post
    Thanks, any ideas why I have alot of moisture under the fan? The insulation is wet, and the emergency pan underneath has a decent amount of water.I will provide a link...on page 16....is a diagram. My unit has the coil reversed....WHY?
    http://crea.com.co/imagenes/PDF/Cat_...60_CATALOG.pdf
    Could be an install (or dirty filter) problem. May have to get someone local to check it.
    Life is too short, Behappy!
    TFMM

  7. #7
    Join Date
    Apr 2004
    Location
    long island
    Posts
    89
    Post Likes
    Thread Starter
    Filter is clean....check out my link. Why does that show the apex pointed toward the fan, away from the return???

  8. #8
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,630
    Post Likes
    Quote Originally Posted by suzook View Post
    Filter is clean....check out my link. Why does that show the apex pointed toward the fan, away from the return???
    What is the model number of your air handler?

    If it isn't a TWG air handler, your link doesn't apply to what you have.

    If you indeed do have a TWG air handler, the apex of the coil should point towards the blower.
    It isn't actually possible to flip the coil on a TWG air handler, without field modifications, and would result in the drain pan being above the coil if the unit is installed with the supply on the left.

  9. #9
    Join Date
    Apr 2004
    Location
    long island
    Posts
    89
    Post Likes
    Thread Starter
    Your right, its not that model. Its the latest vs ah from trane. I just don't understand why the insulation under the blower is wet, along with corrosion on the wire terminals already. Guess I will call the installer back. Any suggestions?

  10. #10
    Join Date
    Jan 2012
    Location
    indy
    Posts
    471
    Post Likes
    Quote Originally Posted by suzook View Post
    Thanks, any ideas why I have alot of moisture under the fan? The insulation is wet, and the emergency pan underneath has a decent amount of water.I will provide a link...on page 16....is a diagram. My unit has the coil reversed....WHY?
    http://crea.com.co/imagenes/PDF/Cat_...60_CATALOG.pdf
    better call your installer, has it done this since day 1? might have a plugged drain which would mean all the humidity in your house is going back into your house and in your unit

  11. #11
    Join Date
    Nov 2004
    Location
    Austin, TX
    Posts
    910
    Post Likes
    As I recall, some of the Trane airhandlers required a larger metal plate be installed at the apex of the A coil for certain configurations. I don't know if the current production requires it as I've not worked for a Trane dealer in 4 years.
    “I am for doing good to the poor, but...I think the best way of doing good to the poor, is not making them easy in poverty, but leading or driving them out of it. I observed...that the more public provisions were made for the poor, the less they provided for themselves, and of course became poorer. And, on the contrary, the less was done for them, the more they did for themselves, and became richer.”
    ― Benjamin Franklin

  12. #12
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,630
    Post Likes
    Quote Originally Posted by allan38 View Post
    As I recall, some of the Trane airhandlers required a larger metal plate be installed at the apex of the A coil for certain configurations. I don't know if the current production requires it as I've not worked for a Trane dealer in 4 years.
    They come equipped with the apex baffle that will work in all configurations.
    For some configurations, including horizontal left, installing the smaller apex baffle increases airflow efficiency, but doesn't affect drainage.