Thread: This unit just had a PM!!
-
08-04-2012, 10:18 PM #1
This unit just had a PM!!
And nothing was quoted except a few shorted to ground compressors. It was the first time anyone from my outfit was on site here & it was obvious that heat rejection was a major issue. i tend to run my hands over everything as i know many of you do & immediately noticed this .. How it was missed is beyond me. I believe 9 of 13 were this bad. I found so much wrong on this inspection i don't think it's all been addressed yet and it was 2 months ago.
Sent from my HTC Sensation 4G using Tapatalk 2
-
08-05-2012, 08:46 AM #2
Professional Member*
- Join Date
- Dec 2002
- Location
- SouthEast NC ICW & Piedmont Foothills
- Posts
- 7,212
don't you just love it
how much whining went on when repairs were quoted
It`s better to be silent and thought the fool; than speak and remove all doubt. 
-
08-05-2012, 08:59 AM #3
Believe it or not the in house guy was all for it because for a long time they had issues with things. Can't say i know the response from those who actually sign the checks lol
Sent from my HTC Sensation 4G using Tapatalk 2
-
08-05-2012, 09:13 AM #4
Looks like a cotton mill
-
08-05-2012, 11:00 AM #5
It's obvious these coils weren't ever split. The discharge temps were through the roof .... I had 3-10 ton circuit severe burn outs, 1 header restriction, few flat systems to name some of the issues. One thing i didn't understand is why they were so focused on getting this building switched over to EMS including brand new VFDs in all units before addressing/spending on the major problems.
Sent from my HTC Sensation 4G using Tapatalk 2