single to a dual circuit
I am changing out a 7.5 ton R-22 single circuit AHU, to a 7.5 ton 410A dual circuit. I know i have to change expansion valve back to R-22. But what else?
-
08-04-2012, 07:03 PM #2
Professional Member
- Join Date
- May 2003
- Location
- Charleston SC
- Posts
- 115
I assume you are changing the outdoor unit to a 2 compressor setup where you will be running at approx. 50% capacity most of the time. I would get the information off the valve and check it out with the manufacturers specs. to see if it will control under reduced volume conditions. If its an OEM valve with no info, you may want to research the Sporlan web site. Its a pain to change a TXV but not as much a pain as callbacks.
Regards
Coolairman
-
08-04-2012, 07:41 PM #3
Regular Guest
- Join Date
- Jul 2012
- Posts
- 19
No! Some people bought a ahu to replace their leaking coil one. Thier old unit is a r-22 single circuit. They were told that no more R-22 AHU 7.5 ton can be found so they bought this dual circuit 410A AHU. I know i can change it over to r-22 but how about the dual circuit?
-
08-04-2012, 07:44 PM #4
2 expansion valves, tee the liquid line together and tee the suction together. mount the sensing bulb to its own suction line for that circuit.
-
08-04-2012, 08:03 PM #5
Regular Guest
- Join Date
- Jul 2012
- Posts
- 19
Ok! Then use two 3.5 ton expansion valves? And also use long radius ells, but how about the tees they will be straight?
-
08-04-2012, 08:40 PM #6
Professional Member
- Join Date
- Aug 2011
- Location
- Salem Oregon
- Posts
- 26
The dozen installs I've seen with tees used regular tees. Though if you are concerned about equal flow, you might put the liquid line into the branch and out the sides to the txvs.
-
08-04-2012, 08:47 PM #7
Professional Member
- Join Date
- Aug 2012
- Location
- Palmyra MO
- Posts
- 198
Just did this last friday.. use two exspansion valves then tee liquid line together. also tee suction lines together and strap bulbs to the suction line before the tee on each circuit separately.
-
08-04-2012, 09:18 PM #8
Regular Guest
- Join Date
- Jul 2012
- Posts
- 19
Ok Thanks will try wed. How about the txv sizes?
-
08-04-2012, 10:02 PM #9
Professional Member
- Join Date
- May 2002
- Location
- evansville indiana
- Posts
- 892
sporlan has decent Tech help...ive been at united trying to select an item and the counter has called them to assist us in selection.
Or download their catalogues and see if you can figure it out,their cats have selection guides.
There is more to it than just tonnage...
if it was me I would call sporlan and explain what I was doing. I bet they will point you in the right direction.... And save a callback or eliminate system issues
Just my opinion...mikeacman
-
08-04-2012, 10:15 PM #10
Professional Member
- Join Date
- Aug 2012
- Location
- Palmyra MO
- Posts
- 198
Get4 ton valves