Thread: 2 HVAC systems, 2 outlet temps
-
08-04-2012, 08:25 PM #14
Trucknorris, this is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise here. Please apply to the AOPC today, thank you.
You can find the rules for posting and qualifications here.
Your post has been deleted.
Further infractions may result in loss of posting privileges.
-
08-04-2012, 10:15 PM #15
Okay, it took a while to find the 16-SEER 2.5-Ton single stage Goodman but here it is: using 85F outdoors; @ 850-CFM; 24,100-Btuh
70F IDB; 59F-IWB or, 52.47% RH; 19F indoor temp-drop, Not 4F, Coil is NOT cold enough to dehumidify.
HI PR 279-psig; Lo PR 124-psig; 2.06-KW; 6.3-amps
If it feels way too humid: @ 1350-CFM 63-IWB 68% RH; 13F temp-drop a lot lower due in large part to increase in humidity latent load; total of 28,000-Btuh.
There are major problems that need addressing; first get a CFM airflow check & get it down to 1000 or even 850-CFM so it dehumidifies.AOP Forum Rules:
Rules for Posting
Rules For Equipment Owners
Equipment Owners Find a Contractor HERE!
udarrell
-
08-04-2012, 10:42 PM #16
Regular Guest
- Join Date
- Jun 2012
- Posts
- 13
Air handler appears to be set for 1020 CFM.
I'll knock it down -15% and see how it changes.
If that is not enough decrease in air flow and assuming for now the charge is proper, would changing the filter to a MERV 13 from a MERV 8 help? My reading through the forums seems to indicate you folks favor the MERV 8. (Unfortunately this system only has provision for 1" filters 16x20)
-
08-05-2012, 07:27 AM #17Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
Use +Merv 10 air filter. -Don't forget the "Golden Rule"
-
08-05-2012, 09:57 AM #18
Regular Guest
- Join Date
- Jun 2012
- Posts
- 13
83 outside.
I dropped the CFM by 15% using the DIP switches on the control board. Outlet Temp went from 68 down to 59 --
73 inlet
Swapped the MERV 8 for MERV 13 Outlet down to 56 - still moving alot of air. We'll give it some time and see how the humidity does.
My thanks to all those that responded and may continue to respond.
-
08-05-2012, 10:29 AM #19AOP Forum Rules:
Rules for Posting
Rules For Equipment Owners
Equipment Owners Find a Contractor HERE!
udarrell
-
08-05-2012, 10:53 AM #20Well, U got the temp-drop to 14F; with a high humidity latent load that could be okay; under normal conditions 18 to 19F would be normal.83 outside.
I dropped the CFM by 15% using the DIP switches on the control board. Outlet Temp went from 68 down to 59 --
73 inlet
Swapped the MERV 8 for MERV 13 Outlet down to 56 - still moving a lot of air. We'll give it some time and see how the humidity does.
My thanks to all those that responded and may continue to respond.
However, a 2.5-Ton 16-SEER; 85-F outdoor temp; 1350-CFM; @75-IDB; 67-IWB, about 67% RH; indoor temp-split would only be 13F...you're at 73F RA temp verses 75F; 83 outdoor verses 85F; we don't know what the actual %humidity is.
With the higher pressure-drop filter; not best option; the drop went to 17F.
If U get the air flow right; low enough; it should begin to dehumidify.AOP Forum Rules:
Rules for Posting
Rules For Equipment Owners
Equipment Owners Find a Contractor HERE!
udarrell
-
08-05-2012, 12:47 PM #21
Regular Guest
- Join Date
- Jun 2012
- Posts
- 13
-
08-06-2012, 08:50 AM #22
Raise the thermostat up 1F and set the fan to "ON" for 30 minutes. Humidity should only go up 2-3%RH... and temperature maybe 1F... unless it's pulling in a lot of attic air. IF when running the fan only you can "smell the attic", then that may answer your question.
-
08-06-2012, 10:13 AM #23
Consider that there is 1 lb. of moisture per ton of coil retained on the coil at the end of the cooling cycle. The moisture on the coil will evaporate back to the home is 30-45 mins. with the fan "on". 2-3 lbs. of moisture into 1,800 sqft. of space will raise the indoor %RH 8-10%.
Regards TBBear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
Use +Merv 10 air filter. -Don't forget the "Golden Rule"
-
08-06-2012, 11:21 AM #24
Regular Guest
- Join Date
- Jun 2012
- Posts
- 13
-
08-13-2012, 08:09 PM #25
Regular Guest
- Join Date
- Jun 2012
- Posts
- 13
So it's been about a week and the humidity is down to 59% temperature outside 85, return 72, outlet 58.
Looking through the manual, there doesn't appear to be anything else I can do to lower the blower speed. -15% CFM DIP switch setting in place and a 1" MERV 13 from Filtersfast.com
Any further suggestions would be appreciated. Thanks guys.
-
08-13-2012, 09:03 PM #26
Professional Member
- Join Date
- Jul 2009
- Location
- Northeast, Md.
- Posts
- 120
At the moment you have a 4 degree split, and that is a major issue! It's time to call a tech out to your home. Regardless of what you think is going on. The system must work correctly before you can fix the other issues.


Reply With Quote