Results 1 to 13 of 27
    Jun 2012
    2 HVAC systems, 2 outlet temps
    My first floor system is an old 10 SEER York 2T installed 1992. Flawless from day one, has only had routine maintenance, capacitor and contactor replaced, 5 2 1 start kit installed. Current temp outside 85 - unit running - air from registers is 57 degrees - works beautifully.
    My second floor unit is a 2 year old Goodman 16 SEER w/variable air handler 2.5T. Current outside temp 85, air output from registers is 68 degrees. (moves way more air than first floor as I guess is expected in a higher SEER unit?)
    Both units have TRION High Voltage electronic air cleaners w/ MERV 8 pre filters. Both have UVC in line.
    Why would there be such a discrepancy in output temps? Why would the second floor always 'feel' more humid though the temps regulate just fine? I can take a 1st vs 2nd floor humidity reading if needed.
    It it just the nature of these higher SEER units?
    68 is not right. And it has nothing to do with seer rating.
    You're either moving WAY, WAY too much air, (doubtful), or there is some other problem.
    A good tech will take several different readings, and should be able to find the problem.
    Austin, TX
    I can think of many different things to cause it to perform poorly.
    The list gets longer the longer I think about it.
    Have a technician take a look at it.
    I am for doing good to the poor, but...I think the best way of doing good to the poor, is not making them easy in poverty, but leading or driving them out of it. I observed...that the more public provisions were made for the poor, the less they provided for themselves, and of course became poorer. And, on the contrary, the less was done for them, the more they did for themselves, and became richer.
    ― Benjamin Franklin
    Massachusetts
    It's difficult to forecast issues when we have very limited info. For example, we know not what the indoor temperature is, therefore we cannot see a temperature drop across the indoor coils. Old units looked for a steeper TD, on the order of 20-25F. Newer units are designed for a smaller TD, 17-20F. So return air temp, on a properly sized, installed and charged system is more of the determining factor in actual supply air temperature. However, the operative work in the previous sentence is PROPERLY. If the system is not properly sized, installed (duct system too) or charged, then all kinds of readings can be affected.
    Goodman 16 SEER units often use a much larger indoor air handler then the outdoor unit. Good chance your installers left it set to factory settings, which is probably moving way too much air.
    Post model number of both the indoor and outdoor unit.
    Jun 2012
    GSC140301A
    AEPF313716
    dip switches set for on 1 2 4 5 6 8
    off 3 and 7
    Outdoor temp 85
    Indoor 73
    starts off slow and then blows alot of air, way more than the York 1st floor older unit.
    Madison, WI/Cape Coral, FL
    Have the tech slow the air flow to obtain the indoor dew point desired. Dropping the temp to 50-55^F is close to the 55^F dew point. This would result in 75^F, <50%RH.
    Regards TB
    Ducts in the attic? That can kill performance right there. If the 1st floor unit has a basement furnace, that helps since the ducts are in a cold basement.
    And as the boys say, high SEER especially with too much air, doesn't give the drop of an oldie.
    Jun 2012
    I can't help where the duct work is located.
    Dip switches are set right. May not be charged right, or something else could be wrong.
    This is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise here. Please apply to the AOPC today, thank you.
    Jun 2012
    The return is 72 discharge 68 outside temp 82
    about 1300 sq ft 4 second floor bedrooms, 2 BR, hallway, 2 story entryway
    (It seems to cool off fine and may be oversized thus not running long enough to dehumidify - I wonder if I reverse DIP 7 and 8 yielding -15% cfm if that would help)
    I can measure the pressures but was afraid I'd violate the DIY rules.
