water temperature sensor calibration device
Hi All -
We've got a lot of 10K-2 immersion sensors wired to our BMS and need to calibrate these sensors. I have heard of NIST temperature calibration tools that insert through a Pete's Plug and directly measure the water temperature to give a point of reference for calibrations/offsets in the BMS.
I've found the Fluke device but wonder if anyone could give a product recommendation?
Thank you.
-
03-30-2013, 11:12 AM #2
Regular Guest
- Join Date
- Jan 2012
- Location
- California
- Posts
- 31
We use one like this when specified. http://www.omega.com/ppt/pptsc.asp?r...000&Nav=vhta05 I don't remember the exact brand but it works well.
-
04-02-2013, 11:51 AM #3
Regular Guest
- Join Date
- Aug 2011
- Location
- Denver PA
- Posts
- 22
I have a Fluke 50D that works well. The company I work for send it out yearly to get calibrated and NIST certified. If you in the Fluke catalog they have probes that can be inserted into a Pete's Plug. I had one i and did it all the time. Sometimes I remove a gauge out of it's well and get my readings.