08-05-2012, 05:24 PM #14
Professional Member
- Join Date
- Mar 2011
- Location
- North Carolina Piedmont Area
- Posts
- 297
As you have found out there is not much to look at when you take apart this type of EXV. It is very unlikely that the push rod is hanging up. As for the power head you will need to leave that to your imagination. The actuator either works or it does not. It only takes at most 30 minute to trouble shoot, that's it. This is where ohms law applies.
An EXV has to be told what to do, If I were you I would not look at it for more than 30 minute in your last effort and final test. Its very clear that your problem lies elsewhere.
This is so basic that on average it should take no more than two hours for a true diagnosis. A decade box would help for sure.
_________________________
Understand the symptoms and you will and you will find a solution.
-
08-05-2012, 08:13 PM #15
Regular Guest
- Join Date
- Aug 2012
- Posts
- 9
sorry on response times computer difficulties
-
08-05-2012, 09:38 PM #16
-
08-05-2012, 11:18 PM #17
-
08-06-2012, 08:16 PM #18
Professional Member
- Join Date
- Mar 2005
- Location
- Indiana
- Posts
- 126
I have three EXVs that I changed out 2 months ago if you still need one.
-
08-06-2012, 10:46 PM #19
Regular Guest
- Join Date
- Aug 2012
- Posts
- 9
Sure do how much do you want and do you have the part numbers
-
08-20-2012, 10:32 PM #20
-
08-20-2012, 11:32 PM #21
Regular Guest
- Join Date
- Jul 2012
- Location
- Southwest
- Posts
- 114
I am not claiming to be a chiller tech, but whats your temp difference across your drier, the shell looking thing before your EXV. Or your air cooled or water cooled unit is seeing freezing cold temperatures... Grab your clamp on, check the temp out of the condenser, then check it before the EXV, is it the same temp, if no, why not?