Results 14 to 21 of 21
    Mar 2011
    Long Beach, CA
    Quote Originally Posted by ed-man View Post
    I'm sure he knows how to expansion valve works he took the head off of it as I said previously and we put it back together thought we may have had it I have worked with him on this chiller for 3 months. Off And. On I think very highly of him. He is just so busy. And. He don't work on chillers every day. I'm just. Thing to help. Him. Cause we will be trying again. Next week
    As you have found out there is not much to look at when you take apart this type of EXV. It is very unlikely that the push rod is hanging up. As for the power head you will need to leave that to your imagination. The actuator either works or it does not. It only takes at most 30 minute to trouble shoot, that's it. This is where ohms law applies.
    An EXV has to be told what to do, If I were you I would not look at it for more than 30 minute in your last effort and final test. Its very clear that your problem lies elsewhere.
    This is so basic that on average it should take no more than two hours for a true diagnosis. A decade box would help for sure.
    _________________________
    Understand the symptoms and you will and you will find a solution.
    sorry on response times computer difficulties
    Quote Originally Posted by supertek65 View Post
    EEV
    electronic expansion valve.
    TEV
    thermal expansion valve
    TXV
    slang for thermal expansion valve
    AEV
    Automatic Expansion Valve
    Apr 2012
    Paper Street Soap Company
    Quote Originally Posted by alcomech View Post
    The trouble shooting methods Trane spells out in their Addendum are pretty straight forward. Keep a stop watch or a stop watch app handy and go into the test submenu.
    That and ohming out the windings and checking the integrity of the cable.
    Indiana
    I have three EXVs that I changed out 2 months ago if you still need one.
    Sure do how much do you want and do you have the part numbers
    show off!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!
    Quote Originally Posted by jayguy View Post
    AEV
    Jul 2012
    Southwest
    I am not claiming to be a chiller tech, but whats your temp difference across your drier, the shell looking thing before your EXV. Or your air cooled or water cooled unit is seeing freezing cold temperatures... Grab your clamp on, check the temp out of the condenser, then check it before the EXV, is it the same temp, if no, why not?