    Mar 2010
    Downriver, Michigan
    What do you think of these numbers?
    Here in Michigan it's 87 degrees outside and the discharge tempature is 52.3 degrees.
    D
    SW Wisconsin
    Indoor supply air temps alone don't tell us what other things we need to know in order to tell how the system is performing.
    What data is needed:
    Performance Data Collection – Best Time to collect data is late afternoon around 4:30 pm, when attic is HOT; also when outdoor temps are around 85; 95; 105F or, anywhere in between.
    *All U need is a good thermometer (digital reading in tenths preferable) & and indoor Humidity Gauge
    1) Helpful; Tonnage & SEER of Unit & outdoor condenser model number: ___________
    2) TXV or, orifice metering device? _______. Only if U know…
    3) Outdoor condenser’s discharge-air-temperature ______-F
    Subtract Outdoor air temperature: _______
    Outdoor Condenser Air-Temp-Split _______
    4) Need the ‘Indoor’ percent of relative humidity - in the middle of the rooms or, at Return-Air inlet grilles ___
    5) Indoor Return-Air Temperature ______
    Subtract Indoor Supply-Air Temperature ______ -F
    Indoor temperature-split _______-F
    We need the above information, plus "a Tech's" Pressure readings & Superheat & Subcooling temps, for troubleshooting & performance analysis.
    Example below:
    A Goodman 2-Ton 13-SEER condenser, 800-cfm indoor airflow; 80-F indoor dry bulb & 50% relative humidity; Indoor temp-split 18 to 19-F.
    @ 85-F outdoors; 103.9-F - 85-F outdoors or around an 18.9-F temp-split;
    @ Indoor 75-F & 50% RH condenser temp-split is only around 14.9-F.
    52.3 degrees might be great, might not.
    Post all the readings you have.
    chicago suburbs
    ill be even more impressed if you tell me your return air temp is 72.3 degrees.
    FILL OUT YOUR PROFILE!!
    Mar 2010
    Downriver, Michigan
    Quote Originally Posted by udarrell View Post
    Example below:
    Thanks for all the information. Thanks to you and my Fieldpiece digital gauges my 25+ year old unit is still running.
    Mar 2010
    Downriver, Michigan
    I just need to turn off the water.