Results 1 to 2 of 2
Thread: Trane VAV
08-03-2012, 08:41 AM #1
- Oct 2005
- 311
Trane VAV
We need to put Trane controls in a Metalaire VAV. I tried to order the VAV-UCM controller but the parts guy only came up with the board, not the pressure transducer (and cable). Anyone know what part(s) I need? Thanks.
08-03-2012, 10:02 PM #2
- Mar 2011
- North Carolina Piedmont Area
- 309
Are currently running Tracer Summit now? if so you will also need to configure UCM controller which I am sure you already know. It sounds like you will be setting the VAV type as a generic box. You will need to match the stroke time for 5-minutes or 90-seconds depending on type which you use.
It is possible to use a standard Belimo actuator 90 second stroke time. However you may have to commission it with the use of the Rover tool, or it may not calibrate correctly- Just a heads up.
Direct Couple Actuator PN: X13611023010
4 Wire Pan cake Motor
PN: ACT417 90-108 Second Motor
Direct Coupled Actuator
Trane X13611064010
Sinro: SRD02-0424A-N6
with wire harness & Connector No Cover- Varitrac
72/60 Seconds 35 Lb
Pressure Transducer PN: SEN0 1465 w/connector
Hope this helps