    No split, but heat rec coil....

    I found a leak today on a condenser discharge header.

    My problem is I have never had to repair one before and was hoping someone could explain the best way to do this.

    4 compressors on an old Hill rack, only one condenser and piped w/ no split.

    The rack does have a hr coil, my question...can I, while monitoring HP, shut down the discharge bv and run the condenser out of liquid, w/ the fans off, then shut rack off, and close drop leg bv?

    Then dump the remaining gas in a pre- pumped down circuit.

    Does this sound right? Or is there a better way.

    Oh yea, There are two other racks w / same R-22 and could dump it in the suction header.

  2. #2
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    20,917
    Quote Originally Posted by sprmktrefertech View Post
    I found a leak today on a condenser discharge header.

    My problem is I have never had to repair one before and was hoping someone could explain the best way to do this.

    4 compressors on an old Hill rack, only one condenser and piped w/ no split.

    The rack does have a hr coil, my question...can I, while monitoring HP, shut down the discharge bv and run the condenser out of liquid, w/ the fans off, then shut rack off, and close drop leg bv?
    Then dump the remaining gas in a pre- pumped down circuit.

    Does this sound right? Or is there a better way.

    Oh yea, There are two other racks w / same R-22 and could dump it in the suction header.
    That isn't going to work.

    I shut the fans down, run the head pressure up to ALMOSt trip point, then shut both BV off and run the recovery machine.

  3. #3
    Join Date
    Dec 2010
    Location
    new jersey
    Posts
    343
    Quote Originally Posted by jpsmith1cm View Post

    I shut the fans down, run the head pressure up to ALMOSt trip point, then shut both BV off and run the recovery machine.
    Thanks, Jp!

  4. #4
    Another tip. Use the recovery machine to pump into the suction header instead of tanks.

  5. #5
    Join Date
    Jul 2000
    Location
    Treasure Coast/Florida
    Posts
    9,743
    Quote Originally Posted by smilies View Post
    Another tip. Use the recovery machine to pump into the suction header instead of tanks.
    I like your thinking. That will speed it up a lot.