  1. #14
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    2,762
    Check the discharge temp if it's like 90. Your flooded!!!

  2. #15
    Join Date
    Jan 2010
    Posts
    5,812
    I will do that when I return. What's a good guesstimate for proper discharge temp ?

  3. #16
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    2,762
    190 sounds good!!!

  4. #17
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    2,762
    What's odd is your low lo side!! If the indoor metering device was bypassing you would think your low side would be higher!!

  5. #18
    Join Date
    Jan 2010
    Posts
    5,812
    I just looked at Carriers troubleshooting chart for this model. It points towards LOW CHARGE for low suction pressure. Or dirty filters,dampers partly closed,duct restricted,indoor coil frosted,liquid line restricted,piston restricted,indoor coil screen restricted.

  6. #19
    Join Date
    Jan 2010
    Posts
    5,812
    Well I'm going to call it a day. I'll keep ya posted how it turns out and thanks for hanging in there with me.

  7. #20
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    2,762
    Quote Originally Posted by VTP99 View Post
    I just looked at Carriers troubleshooting chart for this model. It points towards LOW CHARGE for low suction pressure. Or dirty filters,dampers partly closed,duct restricted,indoor coil frosted,liquid line restricted,piston restricted,indoor coil screen restricted.
    Ok,let us know when you pull out the excess refrigerant and fix the airflow problem!!!

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event