Results 1 to 6 of 6

Thread: what is this?

  1. #1
    Join Date
    Feb 2009
    Location
    Ft Madison IA
    Posts
    33

    what is this?

    this item is on a stainless plate water chiller
    is this to keep the evap flooded? and draws vapor off the top of this tank?
    Attached Images Attached Images

  2. #2
    Join Date
    Oct 2011
    Location
    La.
    Posts
    211
    surge drum. used to keep the cooler flooded and at saturation temp.
    without flooding compressor

    you must be working in a food process facility or bread plant.

  3. #3
    Join Date
    Feb 2010
    Location
    MEXICO
    Posts
    410
    this is more common with ammonia systems

  4. #4
    Join Date
    Mar 2011
    Location
    North Carolina Piedmont Area
    Posts
    297
    Can it be a Vertical liquid receiver?

  5. #5
    Join Date
    Aug 2012
    Location
    Tijuana, Mexico
    Posts
    18
    This is made to keep the evaporator flooded and when you want to recirculate the refrigerant for subcooling.

  6. #6
    Join Date
    Feb 2009
    Location
    Ft Madison IA
    Posts
    33
    yes it is a bread factory, thats good info thanx for the responses

    i see that it is similar to an amonnia vessal

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •