Page 5 of 5 FirstFirst 12345
Results 53 to 59 of 59
  1. #53
    Quote Originally Posted by garyed View Post
    I 100% agree, we seem to have an argument about once a year about whether a liquid line restriction can cause elevated head pressure without the system being over charged. They obviously don't teach that in class so only those who have experienced it in the field can attest to it.
    RTU and a split system are different, hen it comes to having a high head with a restricted LLFD. Microchannel condensers will have a high head as they just don't hold much volume, so there is no room for all the liquid refrigerant to stack up in them.
  2. #54
    Jul 2009
    South Carolina
    From what I've seen the microchannel units act no different than any tube & fin unit. They just hold less gas which makes them more sensitive to charge & they leak a lot. They probably hold the same amount of gas as an older 8 or 10 SEER might. I don't see how that would make that much of a difference. I've pumped down plenty of microchannel units before I ever knew I wasn't supposed to & they pumped down just fine. On long line sets I had to remove some gas first no different than I would any other type of unit. I'm not arguing that they can hold as much gas in the condenser as a regular unit but just that there was already less gas to compensate for in the system if the charge was correct so I don't see how that changes the basic principles.
    Gary
    http://www.oceanhvac.com
    The best things in life are free but not everyone is willing to pay the price.
  3. #55
    Old 8 and 10 SEER condensers could hold a lot og refrigerant. Micro channels can't hold nearly as much. Try pumping one down to itself.
  4. #56
    Jul 2009
    South Carolina
    I don't want to hijack this thread so I'll give up until this comes up in another thread.
    Gary
  5. #57
    IL
    Quote Originally Posted by gravity View Post
    i have a video of a drier i just found restricted. a carrier 28ton rtu. circuit #1 had pressures of 40/600. 600psi before the drier and 250 after the drier. this was a new microchannel coil. no temp split across drier but a pressure drop of 350psi! if i wouldnt have been able to check across that drier i would have said the condenser was restricted.
    Wait? A pressure drop across the filter dryer didnt cause a temp drop? How is that possible? P/T relationship? Being that there is no load on that causing it to gain or lose heat just pressure drop should of cause temp difference? I had one last week that had a 50 degree drop across it, frosted on one side... Must be a rare one then.. Like to know on that, been a service guy for 2-3 years or so now residential and commercial RTU. Please enlighten me. Not saying your wrong at all, just want to learn more! LEARN EVERYDAY!
  6. #58
    Jul 2009
    Columbia, MD
    there is a thread floating around here somewhere describing why you wont always have a temp split.
  7. #59
    Tallahassee, FL
    Hvacrmedic is the guy who wrote what gravity mentioned.
    Another trick is that when the unit has been overcharged the increased sc tends to help mask restrictions.
    So the trick is kill the indoor fan and possibly recover some of charge and that will cause SC to drop which will cause more of a temp drop across suspect part.
