Do notget me wrong iam a advocate of replacing driers ,if i find a unit low charge due to a leak in evap coil and gas it up untill coil can be replaced if there is no indication of a problem with the drier i flat rate it for a pump down. If the drier is inside the unit it stays if it is in the liquid line it gets replaced and i do not add a 2nd drier. If i suspect the unit ran in a vacuum the drier gets replaced ,if it is in a vacuum i dont gas them up
-
08-08-2012, 12:40 AM #44
Regular Guest
- Join Date
- Jun 2011
- Location
- Houston,TX
- Posts
- 11
Just an update,after weighing everyones opinion and recomendations I pumped down the condenser leaving the original llfd and changed the evap coil.Normaly if there is a llfd outside the condenser I would have pumped down the unit removed the llfd and installed a new one at the new evaporator. Thanks for the input this is a good controversial subject like merv 6 filters vs the old fiberglass lol.
-
08-10-2012, 05:59 PM #45
i have a video of a drier i just found restricted. a carrier 28ton rtu. circuit #1 had pressures of 40/600. 600psi before the drier and 250 after the drier. this was a new microchannel coil. no temp split across drier but a pressure drop of 350psi! if i wouldnt have been able to check across that drier i would have said the condenser was restricted.
-
08-10-2012, 06:09 PM #46[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
-
08-10-2012, 06:29 PM #47
Was told in school that every time the system is opened period you replace the drier, weather it had a leak or replacing any part that the refrigerant goes thru.
Sent from my iPhone using Tapatalk
-
08-10-2012, 07:41 PM #48Gary
-----------
http://www.oceanhvac.com
An engineer designs what he would never work on.
A technician works on what he would never design.
-
08-10-2012, 10:59 PM #49
the unit was not overcharged. i weighed the tank when i recovered it and it was exactly what nameplate called for. only thing i can think is the suction piping and evaporator can hold more refrigerant then the microchannel condensor which is why it acted the way it did.
i have seen regular split systems with correct charge show low suction and low hi side pressure due to restricted llfd. i have also seen units overcharged with restricted llfd which shows low suction and really high hi side. each system is different. this is where experience takes over in the field
-
08-10-2012, 11:29 PM #50
I 100% agree, we seem to have an argument about once a year about whether a liquid line restriction can cause elevated head pressure without the system being over charged. They obviously don't teach that in class so only those who have experienced it in the field can attest to it.
Gary
-----------
http://www.oceanhvac.com
An engineer designs what he would never work on.
A technician works on what he would never design.
-
08-10-2012, 11:43 PM #51
text book also teaches to take temp split across driers. i have seen only one drier in my lifetime that was dry on one side and sweating on the other. i have diagnosed all my other driers by taking a pressure difference across it.
-
08-11-2012, 12:01 AM #52
Regular Guest
- Join Date
- Aug 2012
- Location
- NE wisconsin
- Posts
- 188
Our company has had a lot of 3 to 6 year old good man coils develop pin holes, Goodman rep called it formic corosion also said with r 410a so sensitive to moisture anytime the system is opened CUT out the dryer and replace it, never torch it out you would release any moisture it has trapped. Straight from the manufacturer on keeping the warrnty valid.