08-09-2012, 11:00 PM #1
Regular Guest
- Join Date
- Sep 2009
- Posts
- 11
Reversing valve or what?
Hey guys I have a system that's driving me crazy I have what you could call perfect pressures but only 72 degrees suction line temp. Unit pumps down with no problem ,no ristrictions. So I'm already at a new txv and new compressor and same problem. Unit still under warranty. Only thing I can think is reversing valve bleeding ! It's not noisy or stuck
-
08-09-2012, 11:17 PM #2
Professional Member
- Join Date
- Feb 2012
- Location
- EVERYWHERE
- Posts
- 161
If the reversing valve is bleeding by then your suction will get warmer after the valve and the hot gas will get cooler after the valve. Do you have that or did you check.
-
08-09-2012, 11:58 PM #3
Regular Guest
- Join Date
- Sep 2009
- Posts
- 11
About 5 degree difference on suction didn't check hot gas side. But if I manually revese from cool to heat and wait a bit and reverse it again it starts to cool for about 10 seconds but once it stabilizes back to cooling it won't drop from 72 average suction line temp
-
08-10-2012, 12:01 AM #4
Professional Member
- Join Date
- Feb 2012
- Location
- EVERYWHERE
- Posts
- 161
what is perfect pressures and what is your superheat and subcooling?
-
08-10-2012, 12:15 AM #5
Regular Guest
- Join Date
- Sep 2009
- Posts
- 11
Subcoolig at 12 low side 79/80 ( 84 inside house). High side 245/250 , evaporator coil gets completely wet when panels on a/h is opened to check coil behavior. (no signs or behavior of restrictions )
-
08-10-2012, 12:29 AM #6
-
08-10-2012, 12:35 AM #7
Regular Guest
- Join Date
- Sep 2009
- Posts
- 11
Gonna tackle it again tomorrow to see what is temp difference at R V on hot gas , thanks
If I run itin heat the out door coil suction one won't get cold. There for its same behavior for indoor and outdoor coil. It's a Trane heat pump.
-
08-10-2012, 12:44 AM #8
-
08-10-2012, 12:50 AM #9
You'll be spinning your wheels. It's only the temp rise on the cold lines in and out that you need to measure. Bypassing will not cause a temperature difference across the hot lines in and out. If you pour a beer into a lake, does the can fill up with lake water? Thats an analogy. In any case, it isn't the reversing valve. When a reversing valve is bypassing suction pressure runs higher than normal. Your suction pressure is normal.
-
08-10-2012, 05:44 AM #10
Was the LLFD changed out when any of the other parts were changed?
This is R22?
-
08-10-2012, 07:27 AM #11
Regular Guest
- Join Date
- Sep 2009
- Posts
- 11
Yeah r22 new filter drier new txv new compressor , same behavior with both coil if reversed from heat to cool condenser coil won't cool in heating and evap coil in cool. No ristrictions
-
08-10-2012, 07:31 AM #12
Professional Member*
- Join Date
- Aug 2012
- Location
- willowick ,oh
- Posts
- 163
Wow. judging by your first post sir. You should call trane tech support before you replace anymore parts. Make sure your check valves are seating properly and hopefully you changed the dryer. Why again was the compressor changed
-
08-10-2012, 07:45 AM #13
Regular Guest
- Join Date
- Sep 2009
- Posts
- 11
Old compressor every once in a while would trip breaker on start up, new compressor works excellent


Reply With Quote