Results 14 to 19 of 19
    Tijuana, Mexico
    I had that problem once and the problem was the liquid line dryer, y don't remember if this model has it, the other is to check your instrumentation values with other gauges and thermometers, ampmeters.
    MEXICO
    york ys
    a dirty filter drier in these machines causes poor oil return
    Tijuana, Mexico
    i'm sorry, i thought it was a smaller chiller, these machines have an electric flow control and it's contrlled by the optiview considering several parameters, i think it's a control or sensor problem, i had a problem once with a broken cable in the low pressure transducer and it wasn't reading well, it was giving a low pressure value.
    Jan 2011
    Quote Originally Posted by Oscar E & E
    The chiller in question doesn't have an Optiview control panel. It's a style "A" screw that came out before Optiview. This chiller probably was built in 1990-91.
    Quote Originally Posted by servicetrane
    I don't believe the OP has mentioned anything about oil return being a problem.
    Jun 2011
    Detroit, MI
    Actually, the OP does indicate they've lost oil out of the seperator. I wonder if a bunch of oil was added to the machine and is logged in the evap. I know when you loos oil into the evap you can get the transducer error. This could explain the lower than usual delta on the evap but not the out of equal numbers when compared to the cond. May even explain the high pressure if someone added a ton of oil. Personally, I'd probably do as others have suggested and verify the calibration of the related sensors-temp and pressure- garbage in is garbage out. Then let that baby sit for a while and equalize out on temps and check the charge of a load of noncondensibles.
    Jan 2011
    The OP hasn't been on the forum since 8/9. Maybe he could tell us what he discovered.