Page 3 of 3 FirstFirst 123
Results 27 to 29 of 29
  1. #27
    Dec 2011
    Did you try to open exv in run mode? put exv in manual control you can go to full open or closed,when running with manager password.
  2. #28
    Jun 2012
    West Virginia
    I switched drivers and it didn't change anything... I then used manual control in run mode and the valve would move wherever I wanted...I don't understand what is keeping the valve from moving to X number of steps the circuit controler is displaying when in normal run mode.
  3. #29
    Jun 2012
    West Virginia
    found out that I had a faulty EXV. it had me fooled for awhile because valve would work fine until it went to an almost closed step position and then hang up. circuit 2 had same problem. 2 bad exv's sehi 175