Results 1 to 9 of 9
  1. #1
    Join Date
    Mar 2003
    Location
    NY
    Posts
    2,265
    Post Likes

    Jace numeric input

    I want to use a Jace with an expansion module to open a valve for a set period determined by some sort of numeric input from a keypad device or a touch screen. Has anyone done this before without using one of the communication protocols? I only need to compare the time that the valve is open to the time set at the input. The logic for this is fairly simple but I am not sure what if anything I can use to inout the numeric (time) value to one of the universal inputs on the expansion module.

    I am aware that I can use a Auto-Matrix touch screen or a Distech EC-Display to accomplish this but I am trying to avoid having to purchase the drivers etc. to make this happen.

    I chose the Jace to do this because I also have to send e-mail notifications and dry contact alarm outputs based on the operation.

    Any ideas?
    "Controls is a lifestyle not a job" -klrogers

  2. #2
    Join Date
    Apr 2007
    Location
    San Diego, CA
    Posts
    1,536
    Post Likes
    Any touchscreen will require some sort of a driver. (I've used the reveal LCD touchscreen from Honeywell). The poor man's solution would be to use a twist timer as your "numeric" input.

  3. #3
    Join Date
    Feb 2005
    Posts
    1,522
    Post Likes
    how do you want to reset the keypad once the time has passed?

    why not just use a windup timer and read on/off contact?

  4. #4
    Join Date
    Sep 2002
    Location
    Hampton Roads, Virginia
    Posts
    1,895
    Post Likes
    Check out Red Loin

    http://www.redlion.net/Products/Digi...og/Timers.html

    I'm sure they have something you could use, just not sure which one.

    Kevin
    "There is plenty of room at the top because very few people care to travel beyond the average route. And so most of us seem satisfied to remain within the confines of mediocrity." -- Benjamin Nnamdi Azikiwe, first president of Nigeria

    "It's not the customer's job to know what they want." -- Steve Jobs

  5. #5
    Join Date
    Jul 2012
    Location
    Northern NY
    Posts
    121
    Post Likes
    If your looking for a display that you can have the operator use to set a point this is the only JACE direct display I know of on the market.

    http://resources.lynxspring.com/Down...JENE-PCLCD.pdf

    But are you looking for an absolute time( such as turn on valve till July 29th @ 5:00PM) or are you just looking for a 15 minutes from now type timer.

    You could do the later with just a manual spring timer and read as an binary input, or you could use a potentiometer to go between 1 and x minutes based on how far they turn the knob and read in the resistance.

    For feedback you could have a start button then have a LCD display to show time remaining via an analog output.


    a few different options, just not 100% clear on your needs.

    -Jeremy

  6. #6
    Join Date
    Jul 2008
    Location
    Melbourne
    Posts
    1,611
    Post Likes
    What about and Advantech touchscreen with its built-in Bacnet or Modbus drivers?

    the little 3.5" WOP-2035V comes with a software utility for building graphics on it...like buttons and sliders and stuff.
    1 + 1 = 3 ( *** for very large values of 1)

    ...everybody wants a box of chocolates and long stemmed rose

    Be brave. You cannot get eaten by an imaginary tiger.

  7. #7
    Join Date
    Mar 2003
    Location
    NY
    Posts
    2,265
    Post Likes
    Thread Starter
    The customer currently has a spring wound timer but they want something a little more 'sophisticated'. I just need to enter a number for the duration that the valve will be opened. I need to monitor water flow and check that the water does not flow for a longer period that than the set time value.
    Money is not really a factor here. The customer wondered if I could install an iPad alongside the Jace so they can enter the time duration.
    The purpose of this is to be sure that the valve does not stick open or fail in some way and allow flow longer than the set duration.
    The display recommended by kc2dnw looks like an ideal solution. I will look more into that.
    "Controls is a lifestyle not a job" -klrogers

  8. #8
    Join Date
    Aug 2006
    Posts
    126
    Post Likes
    Could you use a potentiometer tied to an analog input on your i/o? This could be used to set the duration.

  9. #9
    Join Date
    Nov 2005
    Location
    Shreveport, Louisiana
    Posts
    2,338
    Post Likes
    Use one of the inputs of your ndio and make it work that way either a potentiometer on an AI or a DI and a software timer.