compressor problems
Semi hermetic with two evaporators at 30 suction 300 highside so taking freon at those readings evaporators are blowing at 48 degrees
-
08-01-2012, 03:00 PM #2
Super heat ? subcooling ?
Temp split across evaporater ?
Evaporaters have solenoid vavles on the liquid lines before the TXVs ?
Sounds like you have unit problems not compressor problems.
Possibly a restriction in air flow or even refrigerant.
-
08-01-2012, 04:17 PM #3
As per the previous post, it's extremely difficult to diagnos a problem with zero information.
I will say this: A compressor operating at 300 psi discharge pressure has quite a reduced capacity compared to a compressor operating at normal discharge pressure at its design condition.
-
08-01-2012, 05:03 PM #4
Next time post less information?

You didn't even state the refrigerant.
Your pressures could be seen as almost normal, if you had 404a, for instance.