  1. #1

    Staring fresh with an indoor pool system install...

    I am a mostly conventional HVAC contractor and I have an opportunity to quote a large pool house with a large, heated 50' X 20' indoor gunite pool. My experiences are limited with indoor pools and mostly consist of troubleshooting an improperly installed LifeBreath unit.

    The pool house is completely separate from the main house and needs to be heated and air conditoned, I am assuming. The owner gave me a competitor's quote and they spec'd a DesertAire system with an air handler, condenser and coil fed by a separate boiler.

    I need some help quoting the proper set up because it will be a nightmare if this doesn't work right as we all know how working for "friends" can turn out.

    What is necessary to heat/cool/control humidity and prevent excessive condensation? Any insight would be greatly appreciated. Please PM or reply to post.

    Rick

    Email Address Removed
    631.655.6808
    Last edited by Chris_Worthington; 09-19-2011 at 02:19 PM. Reason: Email Address Removed

  2. #2
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    6,637
    With a specified system, follow the specs and get a signoff on preformance.
    The biggest miss I see on poolrooms is not having an air tight structure and enough negative pressure to stop moisture from passing out through the insulatio of the building.
    thermastor.com/Pool-And-Spa-Humidity-Control/Pool-And-Spa-Brochure.pdf
    has a good description of simple humidity control in a poolroom.
    Regards TB
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

  3. #3
    Join Date
    Sep 2007
    Location
    Boise, ID
    Posts
    4,395
    DesertAire makes a mighty fine unit. They can be a pain to set up sometimes. Pool's/ Natatoriums are dangerous areas for the novice. The single most problem that occurs is improper water treatment of the pool which destroys the equipment it 3-5 years.

    Did I say that proper water treatment is crucial? You might search DesertAir for white papers, not sure if they have anything like that. In the absence, call them and talk to them about it.
    If a nation expects to be ignorant and free, in a state of civilization, it expects what will never be. (Thomas Jefferson 1816)

  4. #4
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,062
    This is just a suggestion, but contact a company that specializes in indoor pools and sub the work to them. There are a lot of components in the design that need to be followed to have a successful end result.

  5. #5
    Join Date
    Jul 2011
    Location
    Columbus, Ohio
    Posts
    136
    Worked on couple of desert air units and I might as well been woking on the space shuttle. They had a metasis controller and a remote interface panel. if I remember correctly you control to 2 degrees above the pool temp and 60%humidity. Some one will correct me soon.

  6. #6
    The job has been decided and it will be a Desert Aire system. The rep is supposed to come out to the job and help me lay it all out. Wish me luck.

  7. #7
    Join Date
    Jun 2006
    Location
    Charlotte, NC area
    Posts
    87
    Desert Aire is a reputable manufacture. They have very good design procedures which will give a good selection. Make sure you and the owner are aware of the design temperature of the room and the pool that the unit is designed for. The space and pool must be operated at these temperatures or excessive evaporation from the pool with cause all sorts of problems.

    And what Teddy Bear said about proper sealing, vapor barrier, and negative pressure.

  8. #8
    Join Date
    Oct 2001
    Posts
    6,966
    check out Dectron site for design diagrams and perticulars on the installation items critical to prop.ops
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY

  9. #9
    Join Date
    Feb 2008
    Location
    smack dab in the middle
    Posts
    23
    Quote Originally Posted by second opinion View Post
    This is just a suggestion, but contact a company that specializes in indoor pools and sub the work to them. There are a lot of components in the design that need to be followed to have a successful end result.

    I would listen to this guy and if an engineer gets involved I would....RUN. pool rooms are NEVER a good thing to get involved with.

  10. #10
    Join Date
    Oct 2011
    Location
    NJ
    Posts
    149
    You might want to consider DuctSox fabric duct for the duct system. Allows for low ESP fans, keeps the air velocity low, ducts don't sweat because the fabric breathes, duct support is less of an issue (crucial in metal ducts in a natatorium setting, even stainless supports corrode in pool environment), metal duct corrosion is less of an issue (some metallic connector ducts are still required).

  11. #11
    Join Date
    Apr 2010
    Location
    southern california
    Posts
    535
    A lot of great advise given. Have been involved with a few. There are so many issues that need to be addressed. A great understanding of psychrometrics will give you the results you need for a proper design. Pay close attention to windows, duct design(Ductsox is a wonderful product for this application), ventilation rate, exhaust and temperature of the air to pool water temperature. Another huge issue is buildup of chloramides and the potential health risks associated with them.

  12. #12
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,921
    hvacindoorpool,

    This is the Ask Our Pro's forum. In order to post advice here, you must have verified qualifications and have been approved by the AOP Committee.

    You can find the rules for posting and qualifications here.

  13. #13

    Water cooled condenser manufacturers

    Water cooled condenser manufacturers, air conditioner manufacturers india

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event