Results 1 to 9 of 9
Thread: Silly question
    Dec 2001
    Silly question
    If a sight glass is between the receiver and LL solenoid, shouldn't the sight glass be full when the solenoid closes? Why would it be empty?
    I carry a gun because I'm too young to die, and too old to take an ass whoopin
    Jun 2010
    Miami
    What makes you think it is empty?
    Dec 2001
    You can watch it drain after the LLSV shuts
    Jun 2010
    Miami
    That would be before...or after the compressor stops?
    May 2003
    Utah
    Essentially you've got a finite volume (condenser, receiver and portion of liquid line) with some amount of refrigerant in it. For this to be 100% liquid, the refrigerant would need to be at a pressure that is equal to, or higher than the correspoding saturation temperature of the refrigerant.
    When the compressor stops the liquid pressure reduces. Likely you're seeing the pressure fall below the point where the refrigerant would remain as 100% liquid.
    Dec 2001
    Quote Originally Posted by bunny View Post
    That makes sense. Thanks
    Either that or the liquid is physically draining back into the receiver, seeking it's own level as any liquid will tend to do.
    This would depend on the piping orientation.
    California
    Have you ruled out magic yet?
    because I think it might be magic.
    Sep 2003
    North-Central Ohio
    I think it's the magic effect. But seriously, I see this all the time and agree w/ bunny & jpsmith1cm.
    Worry about the site glass when box temp is close and the unit is running. Also pay close attention to SC and SH.