    I have a York chiller (MN: YS CA BB S1 - CG E) and I need to calibrate the valve slide. I can not find any litature on how to do this. I've been referred to York Service Manual 160.81-M1, however, it is only a parts list. Do you have detailed instructions on how to calibrate this slide valve?
    Thanks,

    Charles.

  2. #2
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    I thought the stepper motors on EXV's were self calibrating since they homed to o positon at power-up.

  3. #3
    Join Date
    Aug 2012
    Location
    SC
    Posts
    7
    Post Likes
    Thread Starter
    This isn't an EXV. It's the slide valve on the compressor that controls its capacity.

  4. #4
    Join Date
    Sep 2011
    Posts
    2
    Post Likes
    Hi u can calibrate using dc volt .836dcv at 0% on the potention meter.

  5. #5
    Join Date
    Aug 2012
    Location
    SC
    Posts
    7
    Post Likes
    Thread Starter
    How? I go into the calibrate slide valve screen and the only option I have is start calibration. I push that, and it pops up a message that calibration failed.

  6. #6
    Join Date
    Sep 2011
    Posts
    2
    Post Likes
    U have to manually calibrate at potention meter remove the cover and use your probe and poke on j20 pin on red and black wire using dcv meter and .836dc start to calibrate using small flat screw driver try to turn slowly then u tighten on the potention meter..

  7. #7
    Join Date
    Feb 2010
    Location
    MEXICO
    Posts
    562
    Post Likes
    I hope you serve. good luck

  8. #8
    Join Date
    Aug 2012
    Location
    SC
    Posts
    7
    Post Likes
    Thread Starter
    I appreciate the help and I'll let yall know how it turns out.

  9. #9
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    The service manual you want is Form 160.80-M1. It's the service instruction for the Optiview control panel. M1 are definitely nots parts lists...they are service instructions. Parts manuals have an RP suffix.

    As far as posting detailed instructions in an open forum...I won't do it. Maybe someone else will.

    BTW, the stuff "servicetrane" gave you is for the old style single line panels. You have an Optiview panel, these instructions won't work.

    Calibration will always fail if you do it when the chiller is off. Try it when it's running.

  10. #10
    Join Date
    Aug 2012
    Location
    SC
    Posts
    7
    Post Likes
    Thread Starter
    Every search for service manual 160.80-M1 came up with a 12 page PDF file that just listed part numbers. As for the calibration, I did do that while it was running. It popped a message up saying calibration failed.

  11. #11
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    If you are trying to get M literature from the JCI website you are out of luck. They don't share that information. Put your email address in your profile and I'll email the calibration procedure. None of the advice you've been given is accurate for an Optiview panel.

  12. #12
    Join Date
    Aug 2012
    Location
    SC
    Posts
    7
    Post Likes
    Thread Starter
    Ok, I put my email on the profile.

  13. #13
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    Sent to your email address.

  14. #14
    Join Date
    Aug 2012
    Location
    SC
    Posts
    7
    Post Likes
    Thread Starter
    Ok, got it calibrated. Thank you so much!

  15. #15
    Join Date
    Sep 2012
    Location
    KC,MO
    Posts
    1
    Post Likes

    charlie1776

    Quote Originally Posted by Charlie1776 View Post
    Ok, got it calibrated. Thank you so much!
    I have the same issue. Do you think you can share the info. I could really use the help.
    Of course i cant get it from JCI.

  16. #16
    Join Date
    Mar 2012
    Posts
    9
    Post Likes
    Having same problem calibrating slide valve


    Sent from my iPhone using Tapatalk

  17. #17
    Join Date
    Dec 2013
    Location
    Russia
    Posts
    203
    Post Likes
    +1 want to know how)

  18. #18
    Join Date
    Mar 2011
    Location
    Texas
    Posts
    41
    Post Likes
    Could you email me 160.47-m2? Thanks

  19. #19
    Join Date
    Jan 2011
    Location
    tt, west indies
    Posts
    213
    Post Likes
    Quote Originally Posted by Charlie1776 View Post
    Ok, got it calibrated. Thank you so much!
    Can't calibrate mines either . Plus I'm getting high motor overload

  20. #20
    Join Date
    Nov 2011
    Location
    CO
    Posts
    17,439
    Post Likes
    Or you could all spend time contributing to this forum helping others and participating enough to apply for PRO status.....then beg for material you didn't need until someone else asked about it.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •