    I have a York chiller (MN: YS CA BB S1 - CG E) and I need to calibrate the valve slide. I can not find any litature on how to do this. I've been referred to York Service Manual 160.81-M1, however, it is only a parts list. Do you have detailed instructions on how to calibrate this slide valve?
    Thanks,

    Charles.

  2. #2
    Join Date
    Jan 2009
    Location
    Saint Joseph, MI
    Posts
    5,564
    Post Likes
    I thought the stepper motors on EXV's were self calibrating since they homed to o positon at power-up.

  3. #3
    Join Date
    Aug 2012
    Location
    SC
    Posts
    7
    Post Likes
    Thread Starter
    This isn't an EXV. It's the slide valve on the compressor that controls its capacity.

  4. #4
    Join Date
    Sep 2011
    Posts
    2
    Post Likes
    Hi u can calibrate using dc volt .836dcv at 0% on the potention meter.

  5. #5
    Join Date
    Aug 2012
    Location
    SC
    Posts
    7
    Post Likes
    Thread Starter
    How? I go into the calibrate slide valve screen and the only option I have is start calibration. I push that, and it pops up a message that calibration failed.

  6. #6
    Join Date
    Sep 2011
    Posts
    2
    Post Likes
    U have to manually calibrate at potention meter remove the cover and use your probe and poke on j20 pin on red and black wire using dcv meter and .836dc start to calibrate using small flat screw driver try to turn slowly then u tighten on the potention meter..

  7. #7
    Join Date
    Feb 2010
    Location
    MEXICO
    Posts
    494
    Post Likes
    I hope you serve. good luck

  8. #8
    Join Date
    Aug 2012
    Location
    SC
    Posts
    7
    Post Likes
    Thread Starter
    I appreciate the help and I'll let yall know how it turns out.

  9. #9
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    The service manual you want is Form 160.80-M1. It's the service instruction for the Optiview control panel. M1 are definitely nots parts lists...they are service instructions. Parts manuals have an RP suffix.

    As far as posting detailed instructions in an open forum...I won't do it. Maybe someone else will.

    BTW, the stuff "servicetrane" gave you is for the old style single line panels. You have an Optiview panel, these instructions won't work.

    Calibration will always fail if you do it when the chiller is off. Try it when it's running.

  10. #10
    Join Date
    Aug 2012
    Location
    SC
    Posts
    7
    Post Likes
    Thread Starter
    Every search for service manual 160.80-M1 came up with a 12 page PDF file that just listed part numbers. As for the calibration, I did do that while it was running. It popped a message up saying calibration failed.

  11. #11
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    If you are trying to get M literature from the JCI website you are out of luck. They don't share that information. Put your email address in your profile and I'll email the calibration procedure. None of the advice you've been given is accurate for an Optiview panel.

  12. #12
    Join Date
    Aug 2012
    Location
    SC
    Posts
    7
    Post Likes
    Thread Starter
    Ok, I put my email on the profile.

  13. #13
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    Sent to your email address.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.