    Trane TU software

    I was told by our local Trane office that TU software was not needed to service the UC8000 after the original start up. I know with the Dyna View and Tech View software it was needed to bind and troubleshoot all the LLID devices. Is it true that the TU software is not needed to service the UC8000? Thanks.

  2. #2
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    2,607
    Post Likes
    Quote Originally Posted by phbua392 View Post
    I was told by our local Trane office that TU software was not needed to service the UC8000 after the original start up. I know with the Dyna View and Tech View software it was needed to bind and troubleshoot all the LLID devices. Is it true that the TU software is not needed to service the UC8000? Thanks.
    What is UC8000?? 8000? wow! thats a pretty big number
    There is not better place for the working men than the union! 100% UA the only HVAC union!

  3. #3
    Join Date
    Feb 2017
    Posts
    4
    Post Likes
    Thread Starter
    Quote Originally Posted by valdelocc View Post
    What is UC8000?? 8000? wow! thats a pretty big number
    My bad . Typed an extra 0

  4. #4
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    2,607
    Post Likes
    .......and yes you need TU to bind llid, your local Trane office is full of dung!
    There is not better place for the working men than the union! 100% UA the only HVAC union!

  5. #5
    Join Date
    Feb 2017
    Posts
    4
    Post Likes
    Thread Starter
    Quote Originally Posted by valdelocc View Post
    .......and yes you need TU to bind llid, your local Trane office is full of dung!
    That's what I thought. Thanks for for your help

  6. #6
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    3,100
    Post Likes
    IF you're talking about a centrifugal chiller, then yes. Some other equipment is able to bind through the AdaptiView panel.

  7. #7
    Join Date
    Feb 2017
    Posts
    4
    Post Likes
    Thread Starter
    Quote Originally Posted by Nuclrchiller View Post
    IF you're talking about a centrifugal chiller, then yes. Some other equipment is able to bind through the AdaptiView panel.
    This on an RTAE

  8. #8
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    2,607
    Post Likes
    Quote Originally Posted by phbua392 View Post
    This on an RTAE
    You need TU 8.4 Sp1 or later to bind llid in that screw chiller.
    There is not better place for the working men than the union! 100% UA the only HVAC union!

  9. #9
    Join Date
    Oct 2005
    Location
    USA
    Posts
    513
    Post Likes
    If it's a RTAE you can bind from the front panel. you just need the passcode.


    Sent from my iPhone using Tapatalk
    RTFM!!!

  10. #10
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,760
    Post Likes
    Quote Originally Posted by manny238 View Post
    If it's a RTAE you can bind from the front panel. you just need the passcode.


    Sent from my iPhone using Tapatalk
    X2. Centrifugals are the only AdaptiView machines you can't bind from the front panel.

  11. #11
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    2,607
    Post Likes
    Quote Originally Posted by phbua392 View Post
    This on an RTAE
    Gave you bad info, you dont need TU for binding on a RTAE, got it all mixed up with the thermal protection removal procedure.
    There is not better place for the working men than the union! 100% UA the only HVAC union!

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.