walk in cooler trouble
Hello I have a walk in cooler with one semi hermetic compressor and two evap units pressures are reading 27 suction 300 high outsider temp ranges from 90 to 100 with about 60 percent humidity one of the evaporators continually is freezing up causing the other to eventually do the same could this beer a expansion valve sticking our something else
-
08-01-2012, 09:53 AM #2
What refer?
What do you have for SH?
Is the sight glass clear?
-
08-01-2012, 09:55 AM #3
Comp M#
Evap M#
X-Valve #
-
08-01-2012, 10:05 AM #4
Regular Guest
- Join Date
- Jul 2012
- Posts
- 6
Sight glass is clear no bubbles im not near the unit work two jobs for all the numbers just know that same evaporator keeps freezing up its a 404 unit
-
08-01-2012, 11:11 AM #5
Regular Guest
- Join Date
- Jul 2012
- Posts
- 6
I'll try to get you those numbers today and i'm confused about the reference and what sh is
-
08-01-2012, 05:43 PM #6
-
08-01-2012, 05:46 PM #7
-
08-02-2012, 09:22 AM #8
What type of defrost, what is the schedule? Superheat is required information.
-
08-02-2012, 09:24 AM #9
Regular Guest
- Join Date
- Jul 2012
- Posts
- 6
Thank you guys I got was the txv filters that needed to be cleaned and adjusted
-
08-02-2012, 10:02 AM #10
yeah 99% of the time, it's because you need to adjust the TXV filters.
-
08-02-2012, 10:38 AM #11
-
08-02-2012, 07:06 PM #12
Regular Guest
- Join Date
- Jul 2012
- Posts
- 6
Amen brother
-
08-02-2012, 11:57 PM #13
Professional Member*
- Join Date
- Apr 2001
- Location
- MINN
- Posts
- 932
you guys figered him out quick.