    Hello I have a walk in cooler with one semi hermetic compressor and two evap units pressures are reading 27 suction 300 high outsider temp ranges from 90 to 100 with about 60 percent humidity one of the evaporators continually is freezing up causing the other to eventually do the same could this beer a expansion valve sticking our something else

  2. #2
    Join Date
    Feb 2010
    Location
    In a boiler room
    Posts
    6,340
    What refer?

    What do you have for SH?

    Is the sight glass clear?

  3. #3
    Join Date
    Aug 2002
    Location
    Southold.calm
    Posts
    3,605
    Comp M#

    Evap M#

    X-Valve #

  4. #4
    Join Date
    Jul 2012
    Posts
    6
    Sight glass is clear no bubbles im not near the unit work two jobs for all the numbers just know that same evaporator keeps freezing up its a 404 unit

  5. #5
    Join Date
    Jul 2012
    Posts
    6
    I'll try to get you those numbers today and i'm confused about the reference and what sh is

  6. #6
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    2,740
    Quote Originally Posted by pimpdzl View Post
    I'll try to get you those numbers today and i'm confused about the reference and what sh is
    Refrigerant and superheat

    chuckcrj, next time call it freezone. everyone knows what that is
    Local 597 Service Fitter
    Metal Trade Journeyman

    PAY ME NOW OR PAY ME LATER

    It was working when I left...
    WWFD

  7. #7
    Join Date
    Feb 2010
    Location
    In a boiler room
    Posts
    6,340
    Quote Originally Posted by 2sac View Post
    Refrigerant and superheat

    chuckcrj, next time call it freezone. everyone knows what that is
    LOL

    I do believe this is a DIY thread.....

  8. #8
    What type of defrost, what is the schedule? Superheat is required information.

  9. #9
    Join Date
    Jul 2012
    Posts
    6
    Thank you guys I got was the txv filters that needed to be cleaned and adjusted

  10. #10
    Join Date
    Feb 2008
    Location
    California
    Posts
    1,893
    yeah 99% of the time, it's because you need to adjust the TXV filters.

  11. #11
    Join Date
    Mar 2002
    Location
    fort walton beach fl.
    Posts
    752
    Quote Originally Posted by Phase Loss View Post
    yeah 99% of the time, it's because you need to adjust the TXV filters.
    http://acfwb.com/

    "The best preparation for good work tomorrow is to do good work today"

  12. #12
    Join Date
    Jul 2012
    Posts
    6
    Amen brother

  13. #13
    Join Date
    Apr 2001
    Location
    MINN
    Posts
    932
    you guys figered him out quick.