Results 1 to 13 of 13
  1. #1
    Join Date
    Jul 2012
    Posts
    6
    Post Likes

    walk in cooler trouble

    Hello I have a walk in cooler with one semi hermetic compressor and two evap units pressures are reading 27 suction 300 high outsider temp ranges from 90 to 100 with about 60 percent humidity one of the evaporators continually is freezing up causing the other to eventually do the same could this beer a expansion valve sticking our something else

  2. #2
    Join Date
    Feb 2010
    Location
    In a machine room
    Posts
    7,953
    Post Likes
    What refer?

    What do you have for SH?

    Is the sight glass clear?

  3. #3
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    14,486
    Post Likes
    Comp M#

    Evap M#

    X-Valve #

  4. #4
    Join Date
    Jul 2012
    Posts
    6
    Post Likes
    Thread Starter
    Sight glass is clear no bubbles im not near the unit work two jobs for all the numbers just know that same evaporator keeps freezing up its a 404 unit

  5. #5
    Join Date
    Jul 2012
    Posts
    6
    Post Likes
    Thread Starter
    I'll try to get you those numbers today and i'm confused about the reference and what sh is

  6. #6
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    6,094
    Post Likes
    Quote Originally Posted by pimpdzl View Post
    I'll try to get you those numbers today and i'm confused about the reference and what sh is
    Refrigerant and superheat

    chuckcrj, next time call it freezone. everyone knows what that is
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  7. #7
    Join Date
    Feb 2010
    Location
    In a machine room
    Posts
    7,953
    Post Likes
    Quote Originally Posted by 2sac View Post
    Refrigerant and superheat

    chuckcrj, next time call it freezone. everyone knows what that is
    LOL

    I do believe this is a DIY thread.....

  8. #8
    Join Date
    Jul 2012
    Posts
    33
    Post Likes
    What type of defrost, what is the schedule? Superheat is required information.

  9. #9
    Join Date
    Jul 2012
    Posts
    6
    Post Likes
    Thread Starter
    Thank you guys I got was the txv filters that needed to be cleaned and adjusted

  10. #10
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,090
    Post Likes
    yeah 99% of the time, it's because you need to adjust the TXV filters.

  11. #11
    Join Date
    Mar 2002
    Location
    fort walton beach fl.
    Posts
    795
    Post Likes
    Quote Originally Posted by Phase Loss View Post
    yeah 99% of the time, it's because you need to adjust the TXV filters.
    http://acfwb.com/

    "The best preparation for good work tomorrow is to do good work today"

  12. #12
    Join Date
    Jul 2012
    Posts
    6
    Post Likes
    Thread Starter
    Amen brother

  13. #13
    Join Date
    Apr 2001
    Location
    MINN
    Posts
    944
    Post Likes
    you guys figered him out quick.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.