    Hello I have a walk in cooler with one semi hermetic compressor and two evap units pressures are reading 27 suction 300 high outsider temp ranges from 90 to 100 with about 60 percent humidity one of the evaporators continually is freezing up causing the other to eventually do the same could this beer a expansion valve sticking our something else
    In a boiler room
    What refer?
    What do you have for SH?
    Is the sight glass clear?
    Southold, NY
    Comp M#
    Evap M#
    X-Valve #
    Jul 2012
    Sight glass is clear no bubbles im not near the unit work two jobs for all the numbers just know that same evaporator keeps freezing up its a 404 unit
    Jul 2012
    I'll try to get you those numbers today and i'm confused about the reference and what sh is
    Oct 2011
    Chicagoland Area
    Quote Originally Posted by pimpdzl View Post
    Refrigerant and superheat
    chuckcrj, next time call it freezone. everyone knows what that is
    Officially, Down for the count
    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET
    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them
    In a boiler room
    Quote Originally Posted by 2sac View Post
    LOL
    I do believe this is a DIY thread.....
    Jul 2012
    What type of defrost, what is the schedule? Superheat is required information.
    Jul 2012
    Thank you guys I got was the txv filters that needed to be cleaned and adjusted
    California
    yeah 99% of the time, it's because you need to adjust the TXV filters.