    Who designed a chiller like this?!:)

    Having an issue with a governair screw type chiller. It has 2 (50) ton compressors. #1 has hot gas bypass and should stay running and #2 comes on as demand calls. I'm having trouble keeping #1 on line. Controllers are saying alarm but but no alarms recorded in allerton controller or Siemans apogy front end. No mechanical alarms that need resetting. But unless I put it in hand ( runs normally) or reset the chiller by terminating power that it shuts off and #2 runs.

  2. #2
    Join Date
    Mar 2003
    Posts
    7,321
    governair machines are built to order, and usually pretty reliable. I would suspect there is some condition you are unaware of causing the alarm. why is it going off? install gages and thermos and check charge, subcool, superheat, etc.

  3. #3
    Join Date
    Aug 2012
    Location
    Tijuana, Mexico
    Posts
    18
    Has EXV valves?