Who designed a chiller like this?!:)
Having an issue with a governair screw type chiller. It has 2 (50) ton compressors. #1 has hot gas bypass and should stay running and #2 comes on as demand calls. I'm having trouble keeping #1 on line. Controllers are saying alarm but but no alarms recorded in allerton controller or Siemans apogy front end. No mechanical alarms that need resetting. But unless I put it in hand ( runs normally) or reset the chiller by terminating power that it shuts off and #2 runs.
-
08-05-2012, 06:20 PM #2
Professional Member
- Join Date
- Mar 2003
- Posts
- 7,249
governair machines are built to order, and usually pretty reliable. I would suspect there is some condition you are unaware of causing the alarm. why is it going off? install gages and thermos and check charge, subcool, superheat, etc.
-
08-09-2012, 05:07 PM #3
Regular Guest
- Join Date
- Aug 2012
- Location
- Tijuana, Mexico
- Posts
- 18
Has EXV valves?