    looking for info on high dc bus alarm, voltage goes to 850 on startup, drive book will not go into detail, 486 volts going into drive york ytk4d7f1-csj drive tm-503t b8-46d

  2. #2
    Join Date
    Dec 2002
    Location
    Titusville Florida
    Posts
    341
    Post Likes
    Found problem,Motor grounded. unsure on this alarm on grounded motor.