    You might want to edit ( ) to 2nd
    Why would I want to do that? On a Trane XL16i or AS Heritage 16 system , the control wires for 1st stage cooling connect to Y2 on the furnace control board or air handler LVTB.
    RSES Certificate Member
    RSES-SWRA President
  2. #41
    Quote Originally Posted by markf57 View Post
    However, when he installed a jumper between R and O, the HP delivered cold air when heating from the HP was called. This is just as mark beiser predicted would happen. He is at a loss how to get Comfort-r in HP heating mode. The bald one says he did it.
    To have Comfort-R in the heat mode of the heat pump, the wires for O from the thermostat and O to the outdoor unit need to be disconnected from the furnace control board and connected together directly, usually with a wire nut.
    Then the Jumper is installed between R and O on the control board.
    RSES-SWRA President
  3. #42
    Sep 2006
    Since I'm using an IAQ, can the installer accomplish this by disconnecting the O wire from the furnace control board and leaving the O from the outdoor unit connected to the O terminal on the EIM? There isn't a dedicated wire from the tstat to the O. Then add the R and O jumper to the control board??
    Thanks,
    Mark
  4. #43
    Yes
    RSES-SWRA President
  5. #44
    Smile
    Not according to my diagram. He has a gas furnace that should have "Y" and "Ylo". On the Air handler should say "Y/lo" and "Y/Y2.
    On the 16 series it should be "Y1 to Y on the furnace and Y/Y2 on the air handler to the OD unit yellow. and Y2 is wired through BK to yellow with red tracer on the OD unit.
    On a single stage unit it would be wired to Y or Y/Y2.
    Last edited by second opinion; 11-15-2007 at 04:20 PM. Reason: can't type and read at same time
  6. #45
    On the 16 series it should be "Y1 to Y/lo on the furnace or air handler to the OD unit yellow. and Y2 is wired through BK to yellow with red tracer on the OD unit.
    You need to check the diagrams again.
    The XL16i requires 80% airflow for first stage.
    If you connect Y1 to Ylo in the furnace, with no power to BK, you only get 80% of 50%. That is only 40% airflow, half of what the system is supposed to have in first stage.
    The wiring diagrams and instructons are very clear that first stage goes to Y/Y2.
    RSES-SWRA President
  7. #46
    Confused
    My "BAD" I need to write it before I type it. I was trying to make the point not to wire it like the 19I and got lost in thought. Sorry for any confusion I really do know the difference.
  8. #47
    Sep 2003
    McKinney, TX
    mark is correct on the 16i wiring.