Results 1 to 7 of 7
Thread: microzones and fan status
Hybrid View
-
07-31-2012, 10:42 AM #1
New Guest
- Join Date
- Jul 2012
- Posts
- 5
microzones and fan status
Hey guys i am fairly new to hvac so bear with me.
I am working on a site using microzone ii controllers. The bms is showing a fan failure on the unit while being commanded on. I went to the unit and the fan is running fine. I am use to seeing a current switch on the unit which sends the signal to the bms showing that the fan is running.
They are telling me here there is no such current switch.
What am i missing that is ovbiously not working to show status.
-
07-31-2012, 10:51 AM #2
New Guest
- Join Date
- Jul 2012
- Posts
- 5
i am looking for a pressure switch after the supply fan an cannot find that either.
-
07-31-2012, 11:02 AM #3
It might be a fan relay failure ( contacts welded shut ), a control module out put failure.
Or there could be a differential pressure switch sending the input back ( unlikely ) or your zones are mixed up.
-
08-01-2012, 11:34 AM #4
Does the fan have a VFD? If so fan status would probably come from one of the status relays in the drive,
-
08-04-2012, 07:27 AM #5
Professional Member
- Join Date
- Mar 2008
- Location
- NC
- Posts
- 1,334
Sounds like you need to find the drawings, or go to the controller and start following wires.
-
08-04-2012, 09:18 AM #6
Maybe that's the problem.........no one ever installed anything to prove the fan?
-
08-07-2012, 03:32 PM #7
check and identify your DI points on the controller, What does your other Microzones say on the front end? do you have a front end? its either an amp ring or pressure switch but must likely an amp ring.