Thread: Heat problem-6 months to fix

  1. #1
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,568
    Post Likes

    Heat problem-6 months to fix

    I have 6 months to figure this.

    While fixing ac, costomer wants me to fix problem before winter.

    Carrier 80% power draft. HO complains furnace limit trips off during windy conditions. Claims this happened after reroof and replaced Bvent pipe.

    8 feet of bvent with one 90 and cap.

    Two service companies said termination cap needs to be extended higher. It is 12" off roof.

    I cannot believe this is the solution with a power induced burner.

    Anybody seen this as a reason to trip off limit.

  2. #2
    Join Date
    Aug 2011
    Location
    Ontario
    Posts
    386
    Post Likes
    you have flame rollout caused by venting or heat exchanger. If venting is sized properly and heat ex is good, than I agree with extending vent another couple feet. Also could be a weak rollout switch.
    There is no bad beer, some just taste better than others.

  3. #3
    Join Date
    Jan 2007
    Location
    Mn the state where absolutey nothing is allowed
    Posts
    2,516
    Post Likes
    or you could have negitive pressure issues in the mech room when the wind blows.

    ive seen that when the vertical vent is on the windy side of the house and the fresh air intake is on the back side of the house which will experience a lower pressure condition causeing your down draft.

    he's lucky he has a furnace with that safty.


    now does he also have a water heater common vented???
    my boss thinks its possible to repeal the laws of physics

  4. #4
    Join Date
    Jan 2007
    Location
    Mn the state where absolutey nothing is allowed
    Posts
    2,516
    Post Likes
    i reread you post...

    12" above roof line is too low. i believe it needs to be 2 ft above anything 10 ft away horizontaly.

    i think that rule has been amended. send a shout out to hearthman for clarification.

    he's the resident expert on all things venting here on this site
    my boss thinks its possible to repeal the laws of physics

  5. #5
    Join Date
    Feb 2004
    Location
    michigan
    Posts
    677
    Post Likes
    Have you seen the limit trip or is it the homeowner that diagnosed the limit? If you think it through,an extreme vacuum, as would be created when it's very windy won't cause the heat exchanger to over heat nor will it cause the flame to roll back out of the heat exchanger. It will cause just the opposite effect, sucking the flame throught the heat exchanger too fast. If it were me I would be looking at flame lift off from the flame rod causing the flame to drop out and the furace to recycle. Is this what is happening, the furnace recycling? A roll out switch has to be manually reset so thats easy to rule out. If it is a flame rod lift off adding a little height to the chimney will help. Supposed to be 2ft taller than anything with in 10'.
    I am the "Wally". All others are meer imitations of the original.

  6. #6
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    If this is the typical 80% induced draft furnace, the vent system is still a natural draft system, that operates at a slight negative pressure. Once the furnace lights, the draft inducer is just dumping the combustion products into the vent system, it isn't blowing them down the vent pipe.

    With an improperly terminated vent pipe, high winds can cause high or low pressure conditions at the vent pipe termination.
    The draft pressure in the vent system should ideally only be in the -0.02 to -0.04"wc range, so adverse pressure conditions at the vent pipe termination can easily cause to much draft, or stop the venting altogether, depending on the conditions.
    Either one can cause the furnace to shut down on one of several safety controls.

  7. #7
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,568
    Post Likes
    Thread Starter
    This is a power draft, not induced draft,system. You cannot tie this to any other vent.
    Other service company showed HO how to reset safety. Unit is in attic.

  8. #8
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    22,111
    Post Likes
    If it is power draft vent terminatin won't make any differance. If it is induced draft like a normal 80% then yes it could. Tremination should be 2' level from the top of the pipe to the roof or higher. If the vent is with in 10' of any obstruction or roof peak thenit needs to be 2' above that obstruction or peak.

    Are you sure you don't have an airflow problem? I would look at airflow before vent on this issue.

  9. #9
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,903
    Post Likes
    Quote Originally Posted by ch4man View Post
    i reread you post...

    12" above roof line is too low. i believe it needs to be 2 ft above anything 10 ft away horizontaly.
    Questions regarding potential surfaces that could deflect a draft down the pipe-
    Are there any walls within 10 feet of the vent termination?
    Also what is the approximate pitch of the roof?

  10. #10
    Join Date
    Nov 2000
    Location
    Indiana
    Posts
    336
    Post Likes
    If it is truly power vented, then the termination should not make a difference but then it would also not make much sense that the problem started after re-roofing. Type B vent is also not the correct material for a system with a positive pressure in the vent.

    If it is a Category 1, mid-efficiency appliance, then the 3/2/10 rule for chimneys doesn't apply either (2 foot above anything within 10 feet). For Type B vent, being a minimum of 8 feet from a vertical wall, the minimum height above the roof penetration for a flat up to 6/12 pitch is 1 foot. Reference Figure and Table 12.7.2 in the NFPA 54 book.

    Most of the problems I have seen like this have more to to with where the termination is located than anything else. Is it located in a "pocket" on the roof? A "zone" that gets pressurized depending on which direction the prevailing wind comes from. Single story garage roofs beside a two-story house is a great example. Wind, most of the time, will help a vent system operate unless it creates a pressure zone on the roof that is at a greater pressure than the attic. So, it may be that increasing the height would help.

  11. #11
    Join Date
    Feb 2004
    Location
    Ontario
    Posts
    701
    Post Likes
    I've seen a couple of cases where roofers sat on or somehow crushed down the B vent cap restricting the venting. Worth checking.

    BTW, are you referring to the high limit, a vent safety switch, or a roll-out switch?
    Question authority!

  12. #12
    Join Date
    Jul 2005
    Location
    Boston/Cape Cod
    Posts
    65
    Post Likes
    Start with a manual for unit, make sure it's the way it should be. By change is house on water?

    P.S. Something like this a while back on the water, winter storms, used a gas draft regulator to "solve" the problem as it was a draft inducer system.
    southshorejohn

  13. #13
    Join Date
    Jan 2007
    Location
    Mn the state where absolutey nothing is allowed
    Posts
    2,516
    Post Likes
    please post the model number. ive never seen a carrier cat II or III furnace. id like to check out the I/O manual.


    or does this have an add on power venter such a tjerland unit?


    tia
    my boss thinks its possible to repeal the laws of physics

  14. #14
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    Quote Originally Posted by timjimbob View Post
    This is a power draft, not induced draft,system. You cannot tie this to any other vent.
    And it has B-vent?

  15. #15
    Join Date
    Jan 2006
    Location
    Powell River, BC, Canada
    Posts
    763
    Post Likes
    What is the model # of the furnace? I worked for Carrier/Bryant dealers for almost 15years and never saw a true 'power vent' model. What kind of 'power draft' are you talking about? B-vent is NOT allowed for positive pressure venting so unless the 'power vent' is right at the termination and pulling through the entire length of b-vent it is illegal and potentially dangerous! Canadian code for b-vent termination is minimum 2' from the roof penetration (on the high side if a sloped roof) AND 2' above anything in a 10' radius.
    Where are you? Are you done yet? I got ONE more call for you.....

  16. #16
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,568
    Post Likes
    Thread Starter
    gasguy, combustion blower is in the furnace. This, I assumed, created a positive pressure up the B vent.
    I have no model #. When it is 150 degrees in the attic, heat problems can wait!

  17. #17
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by timjimbob View Post
    gasguy, combustion blower is in the furnace. This, I assumed, created a positive pressure up the B vent.
    I have no model #. When it is 150 degrees in the attic, heat problems can wait!
    Just a standard induced draft furnace then. The B vent is a negative pressure vent. So the height above the roof and anything within 10 foot of it is very important.

    Its probably tripping the rollout as said by others. And the venting needs corrected.

    Being so close to the roof, wind can cause a down draft.

  18. #18
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    Quote Originally Posted by timjimbob View Post
    gasguy, combustion blower is in the furnace. This, I assumed, created a positive pressure up the B vent.
    I have no model #. When it is 150 degrees in the attic, heat problems can wait!
    That is just a regular induced draft furnace, not a power vented furnace.
    Since it is a Carrier furnace, the limit control that is tripping is likely the vent temperature limit.
    With an improperly terminated vent system, the vent temperature limit tends to trip when wind conditions are interfering with the drafting of the vent system.

  19. #19
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,568
    Post Likes
    Thread Starter
    I still have alot to learn. Is bvent under positive pressure?

  20. #20
    Join Date
    Jan 2006
    Location
    Powell River, BC, Canada
    Posts
    763
    Post Likes
    NO. The draft inducer fan is only meant to overcome the resistance of the HX. It's called induced draft as it pulls the gasses through the HX from the exhaust end as opposed to a power burner (think oil burner) which pushes in from the burner end. I agree that you need to lengthen the b-vent and you may need to install a high wind style cap.
    Where are you? Are you done yet? I got ONE more call for you.....

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •