    Trane 16X LS service valve - how do they work?

    What's up with the service valve on the low side of the monster Trane 16X, Mfg 9/2010?

    I walked up to one today that would not start despite high and low voltage. Chased the control voltage past the delay and up to the small apartment that is the coil and quickly decided it has to be a LP or LOC switch. Hook up and go to open the valves and there is this odd rectangular deal on the low side with stops on it - like you can only turn it a quater or a half.

    How does this valve work? Quarter or half turn down to open to gauges? What if you have to pump it down or isolate the condenser?

    I might end up going back as there was oil all over the suction line at the evaporator coil. But the client is understandably going after the installing contractor first. It was only installed about 18 months ago.

    Even though there is literally nothing left to recover, how do you close these Trane low side valves to isolate, leak check, repair, pressure test etc?

    The high side valve appeared to be a regular service valve.

    Appreciate any help as always,

    h

  2. #2
    Join Date
    Nov 2011
    Location
    Phoenix,AZ
    Posts
    317
    assuming its like all the ones i've seen its a 1/4 turn open to close

    it has a regular schrader core for gauges

  3. #3
    Join Date
    Apr 2010
    Location
    Minnesota
    Posts
    517
    It's a ball valve.

  4. #4
    Join Date
    Jul 2009
    Location
    Ontario, Canada
    Posts
    913
    Quote Originally Posted by dunkman View Post
    It's a ball valve.
    usually a 1/4turn ball valve. Lennox also uses this on some of their larger units, usually 3tons and up.

  5. #5
    Join Date
    Jul 2006
    Location
    Virginia
    Posts
    4,676
    Trane use the 1/4 turn ball valve on most of their suction service valves

  6. #6
    Join Date
    Nov 2011
    Location
    St. Louis
    Posts
    3,442
    OK...I see.

    System was completely flat - the ball valve was actually already open when I hooked up.

    Thanks all.