Results 14 to 16 of 16
    But he's talking about 3 cool, 2 heat. The vision pro IAQ will do 4heat, 2 cool. But I haven't seen one that will do 3 cool, there's not much demand for it.
    He corrected himself, and said its 3 heat 2 cool.
    Jul 2010
    nebraska
    3h2c
    Quote Originally Posted by jjmarquez84 View Post
    I helped install a new residential multistage heat pump system that was equipped to provide three stages cooling with two stages of heating. To be honest I really dont understand how all the stages of heating and cooling were to be accomplished by the t-stat. I guess its something that I never picked up, or really understood but what I don't understand clearly is how or what controls the stages? Any takers?
    Fairly simple for a good thermostat/thermidistat. First stage cool brought on by temp rise,second stage brought on by higher temp or time depending on how the stat is set up. Heating will be the same with an outdoor temp sensor or two in the mix to determin which stage to bring on.
    Our house (has 4h2c) for example is set up to bring on 1st stage cool with a 1 degree rise and second stage cool with a 2 degree rise. If the humidity is above 50% then it runs second stage compressor but leaves the blower on first stage cfm. The heat pump runs seconds stage if the outdoor temp is between 32 and 50, first stage hp only if it's over 50,first stage gas if it's 31 or less and second stage gas if the stat falls 2 degrees below set point.
    Saint Joseph, MI
    One simple solution for 3 cooling stages is to use the dehumidification terminal to drop out 2nd stage. Otherwise you normally cycle between 2nd and 3rd stages. The airflow would have to by managed by the air handler(s). But airflwo requirements would depend on how many refrigerant circuits it has and how the coils are configured.